oh dear, oh dear.....
An unexpected power cut tested out the new installation today...and I am not happy
The whole point of using this expensive system was to prevent interruption of the supply to the house
The website https://fox-ess.uk/eps-box-sp-backup-gateway/#eps-more makes a point of, and clearly states that it provides uninterrupted power, changes over instantly, seamlessly and without interruption
I quote:
Whole home backup for residential storage installations
The Fox ESS EPS-BOX-SP is a single-phase whole home backup gateway that provides uninterrupted power during grid outages. Designed for single-phase installations, it automatically switches between on-grid and off-grid modes to keep your essential (or all) household circuits running without interruption.
How it works
The EPS-BOX-SP sits between your Fox ESS inverter, utility supply, and household circuits.
Normal Operation – When the grid is active, power flows normally from your solar and grid supply.
Power Outage – The EPS-BOX-SP instantly disconnects from the grid and switches to your battery and solar supply, maintaining power to your home.
Grid Restoration – When the grid returns, it seamlessly reconnects and resumes standard operation.
...except that it doesnt....when the power cut happened the whole house went off, then a few seconds later (!!!!) the supply to the house resumed from the battery......when the power came back again the same thing happened
I later ran the test again this time using the supply isolator switch to give a clean break and exactly the same happened.....router died, NAS offline, CCTV offline, PC shutdown potentially with open files then went offline etc. etc
Even this says the switchover time is only 20mS
https://www.google.com/search?q=fox+kh7 ... fId=ChxjMe
This is exactly the scenario I was hoping to avoid!
Completely unrelated but it is now pitch dark but the panels are showing 240V albeit at zero current...
FOX KH7 7kw hybrid inverter
EN-EPS-BOX-SP gateway
You are obviously upset, but what Inverter do you have, and what errors are showing on the screen?
If you have a small 3.68kW Inverter and 5kW load, it won't handle it.
If your battery SoC is not enough, it won't work either.
Then theres the chance they wired things up wrong.
If you can provide more details, then some help can be given hopefully.
Hi, indeed I am not happy.....
system comprises:
14 x Aiko Neostar 2p plus 475W panels (6.6 kWP)
Fox EP12 10.4kW usable battery (>40% SOC)
Pretty much all perfectly matched as far as I can tell...
system comprises:
Same inverter as mine, should be able to handle 7kW EPS load... unless you was using more than that at the time.
Do you have fault codes on Inverter screen?
I would expect grid loss and Voltage warnings to be stored (and usually in the FoxCloud2.0 App you can view once running) on the Inverter screen/history.
No errors or messages
Load was maybe 3 or 400 watts no more
Sounds like you need to chase the installers down to check into this.
I added UPS to all the important items, don't want my NAS to turn off either
I have had three UPS running for years.....one on the PC & bband /wifi, one on the TV and AV system, one kn the CCTV etc.....as well as going solar I opted for the Fox gateway in order to get rid of the UPS and their expensive battery replacements
The specs clearly state NO break and elsewhere 20mS which is fine....not the several seconds I am getting
The wording in the page you link to is somewhat misleading, the EPS Box has a transfer time of "less than 3 seconds" according to the user manual https://theecosupermarket.co.uk/wp-cont ... 9VBc9c.pdf. As it uses an electromechanical changeover switch there is no way it can achieve a 20mS break.
The 20mS changeover is only mentioned in the inverter documentation for the EPS output.
So if I've read it correctly, the only way to achieve a 20mS maximum break time is to run the inverter as a UPS, directly feeding the load from the EPS output, with the EPS output set to operate in UPS mode.
Manager(ARM):1.69
Master:1.51
BMS:1.012
Manager(ARM):1.69
Master:1.51
BMS:1.012
yep, the inverter IS set to UPS mode
That makes the EPS output act as a UPS output BUT it is only connected to the load by the EPS box in the event of an incoming mains failure being detected by the changeover relay in the EPS box, hence the delay.
Manager(ARM):1.69
Master:1.51
BMS:1.012
Manager(ARM):1.69
Master:1.51
BMS:1.012
well that makes it totally pointless having ....
the whole point of the expensive whole home EPS we bought was to eliminate the breaks - exactly as the description would have you believe
we get quite a lot of power cuts and brown-outs hence the desire for the system we bought
I understand the requirement to have the inverter wired through the gateway to prevent it back-feeding to the grid in the event of a power cut but if what you are saying is correct then how can the house ever be proper UPS
If you check out Will's video, he tests a different switch box, and as you can see, it works how you want it to be.
Depending on what was said in your emails with the Installers, you may have a leg to stand on if you was told it would be instant.
@nrb501, thanks for the PDF, I did look and download last night, but my tired eyes missed the "3s" line in the PDF.
It does look like the Eco-ESS box will fulfil your needs - at least time delays and voltage parameters are configurable if required. It looks like the Fox EPS box just uses a cheap non-configurable automatic transfer switch.
Basic manual for the Eco-ESS box https://www.eco-ess.co.uk/wp-content/up ... ev-2.3.pdf
Manager(ARM):1.69
Master:1.51
BMS:1.012
Manager(ARM):1.69
Master:1.51
BMS:1.012
Hmmm...problem is i dont want to shell out more £££" to find it diesnt
The Fox one clearly and unambiguously states what it should do......
Have you checked emails to/from your installers to see how you/they have worded how your system will work?
If you asked for UPS like function and they didn't deliver, then they need to fix this.
If you made the mistake, sadly this could be on you utimately.
@ntb501....
thanks for the info
The manual states
When the mains grid supply returns to a healthy state the EPS-ATS will disconnect the emergency
power supply from the customers load before re-engaging the mains grid back to the customers
load after a 20s delay
am I reading this wrong or does that mean 20 sec with no power to the house ?
I still feel the Fox info is misleading and wrong...
thanks for the info
The manual states
The system will monitor the incoming grid for a stable Voltage for 20s before it will switchover from EPS to GRID mode.davidwf15 wrote: ↑Wed Apr 01, 2026 11:27 pm When the mains grid supply returns to a healthy state the EPS-ATS will disconnect the emergency
If the outside grid is not stable, the switchover won't happen.
You won't be without power for 20s.
I thought that would be the case
worst case scenario would entail buying 3 x small UPS's for the few seconds they would be needed.....I previously had two huge APC pure sine wave units, an SUA1000i running the TV/broadband/wifi and an SUA1500i for the PC, NAS and CCTV........I fitted them with external 38 and 45AH batteries which ran everything for several hours - certainly long enough for the power cuts (both for sale if anyone interested)
I guess for the few seconds they would be needed the cheaper and smaller stepped sine wave type would suffice
I still feel cheated and mis-sold at the wording on their websites though as it clearly and unambiguously states it provides a no break supply
I have logged a ticket with support to see what they have to say