Hello, my system has been running for about 14 days now, and I am not very satisfied with the connection to Home Assistant via the cloud. I have now purchased a Modbus gateway for this purpose. Earlier today, I unscrewed the plug for the meter to check how much effort the cabling would require. I noticed that this connection is done with a LAN connection on the inverter. Other then expected. The smart meter (which is unfortunately not correctly connected to the grid) is already connected there with the LAN cable. I haven't found anything about this online yet. Can I assume that the wires on pins 1 and 2 are the correct ones? Has anyone else connected it this way before?

Best regards
Marc
Re: H3-12.0-Smart Modbus Connection
I assume when you say LAN cable, that they've used cat5 cable and it isn't an ethernet RJ45 plug ?.

I think you are looking at the meter connector and on the H3 Smart the RS485 pins for the computer have been moved to the much larger 'COM' connector and they have called them EMS 485A/B - those are the pins you need to connect to.
Re: H3-12.0-Smart Modbus Connection
2025-08-29 10_12_53-PXL_20250826_084533588.jpg bei 50% (RGB_8) _.jpg
You mean this one?
Re: H3-12.0-Smart Modbus Connection
No that's where the datalogger plugs in and Fox have un-helpfully labelled it the COMM/Dongle port

This is the COM port
111.jpg
And these are the pin outs for it.
222.jpg
Re: H3-12.0-Smart Modbus Connection
Hi all,
Please let me jump onto this topic.
My new H3-10.0-Smart inverter gets installed today and I would like to set up modbus for Homeassistant and EVCC.

I have purchased an elfin W11a and understood that this needs to be connected to the ems485a/b ports of the com connector.
However, which pins do I need to connect the 12V power +/- ?

A second question: EVCC integration for the H3-smart also list „modbus tcpip“ option.

# Modbus TCP
modbus: tcpip
id: 247
host: 192.0.2.2 # Hostname
port: 502 # Port

Does this mean the RS485 dongle ist not needed to set the H3-smart up in EVCC?
Does this only work for EVCC or also for home assistant?

Thanks for your comments.
Re: H3-12.0-Smart Modbus Connection
Hi,

I connected a serial/LAN adapter with an external power supply. One from the big A. USR-TCP232-304 works fine for me.

The option to attach the Fox inverter directly with the ip doesn´t work for me. And as far as i understood there is no option - at the moment - to connect with homeassitant directly to the inverter.

BR
Marc
Re: H3-12.0-Smart Modbus Connection
Hi Marc,

Thanks for your feedback.
I have got a RS485 to wifi adapter.
I guess you connected yours to an external 12V DC power supply?

I know that the H3 inverters had the option to use a built-in 12V connection to supply the RS485 adapter. I am now wonder which ports of the com dongle of the H3-smart to use to connect to 12V.

In the screenshots above, there is a +12V port (#12). I wonder if this plus one GND port are the correct ones.
Re: H3-12.0-Smart Modbus Connection
Nelbjo wrote: Mon Oct 06, 2025 11:13 am
In the screenshots above, there is a +12V port (#12). I wonder if this plus one GND port are the correct ones.
There is 12v out on the connector which is used to power the Fox EMS unit, it's not very powerful, we believe around 300mA max current - most people use an external 12V 1A power supply as the Elfin can be a little fussy about it's power source (don't forget with RS485 pairs the Elfin can be wired some distance away from the inverter if you use good quality shielded cable ~cat5/6 which might make finding power easier).
Re: H3-12.0-Smart Modbus Connection
Thanks for the good info. OK - then presumably it’s better to get an external power supply.

I intended to use an old USB cable for connection. I still have plenty of cat 6e installation cable (the orange one with solid wires) - can I use that one for the RS485 connection?
Re: H3-12.0-Smart Modbus Connection
Nelbjo wrote: Mon Oct 06, 2025 1:12 pm Thanks for the good info. OK - then presumably it’s better to get an external power supply.

I intended to use an old USB cable for connection. I still have plenty of cat 6e installation cable (the orange one with solid wires) - can I use that one for the RS485 connection?
I've never used the Elfin myself but a few years back there were a number of people that used the USB power that was on the Gen 1 inverters, it didn't work well and so they went to a distinct power supply - there's obviously no harm in trying it but you'll need to keep the Elfin in an enclosure nearby and I do know they don't like extreme cold, if you can run a longer cable and use a good power supply i'd do that.

No problem using Cat 6e but make sure you use a 'pair' i.e. orange and orange/white, some installers have used 2 pairs one pair for each core but that doesn't give you the common mode noise rejection a single pair does.
Re: H3-12.0-Smart Modbus Connection
Thanks Dave, excellent.
So if understood correctly you recommend I use only one twisted pair?: e.g.
- orange for 485A
- orange/white for 485B
Re: H3-12.0-Smart Modbus Connection
Nelbjo wrote: Mon Oct 06, 2025 1:26 pm Thanks Dave, excellent.
So if understood correctly you recommend I use only one twisted pair?: e.g.
- orange for 485A
- orange/white for 485B
Yes that's it, it doesn't matter which pair you use as long as you use a twisted pair (i.e. single color & same colour with white stripe)
Re: H3-12.0-Smart Modbus Connection
Hi Dave,

I would like to ask you about the wiring of the COM connection. I am looking at the COM port at the inverter and I see 24Pins (as mentioned in the manual for the H3-12.0 Smart). I am confused by where to connect any wires for the 485A and 485B since in the manual under 6.10 are only 16 slots shown and named. Is it possible that there should be a plug for the COM port that has a different pinout then the COM port directly at the inverter through which I need to connect the Elfin wires?

Thanks for your help in advance
Re: H3-12.0-Smart Modbus Connection
smarthomie wrote: Fri Jan 23, 2026 2:09 pm Hi Dave,

I would like to ask you about the wiring of the COM connection. I am looking at the COM port at the inverter and I see 24Pins (as mentioned in the manual for the H3-12.0 Smart). I am confused by where to connect any wires for the 485A and 485B since in the manual under 6.10 are only 16 slots shown and named. Is it possible that there should be a plug for the COM port that has a different pinout then the COM port directly at the inverter through which I need to connect the Elfin wires?

Thanks for your help in advance
If you are connecting by RS485 by modbus, you need to wire to the EMS485A/B pins
IMG_1794.png
But with the H3 Smart you can connect directly to it without a modbus device as it has a built in modbus server on the wifi logger, try connecting to the inverters IP address using the integrations direct LAN mode.
Re: H3-12.0-Smart Modbus Connection
Thanks for the quick reply.
I have a somewhat complicated setup. My raspberry pi running homeassistant is connected to my home network via a wireguard server hosted by my fritzbox. It shows up as a internal network device and I am also able to ping the internal ip adress of "solarmanager" which is supposedly the name of the inverter in the list of devices that are connected to my router. But when I am trying to connect the "FoxEss - Modbus" integration on home assistant with the ip adress of "solarmanager" it gives me an error:

Unable to connect to your inverter. Make sure the connection details are correct and try again. Details: Connection to (192.168.1.xxx, 502) failed: [Errno 111] Connection refused

I also checked the inverter slave ID in the inverter menu which is 247. When I clicked through the inverter menu to check the inverter slave ID I realised that under "Settings --> Communication" there are two options: "Ethernet" and "Modbus". I found a manual by SMARTFOX where the process of integrating the inverter to a cloud system that controls the chargingprocess in relation to the market price of kWh is described. In this manual it says that there should be two options "Ethernet" and "RS485". Is this a question of which version I have? Do I have to activate the modbus server somehow?

EDIT:

I managed to connect the H3-Smart inverter to homeassistant by try-and-error. I tried to connect every local IP adress in my routers "active device" list and eventually figured out that the inverter modbus server is called "espressif" and NOT "solarmanager". Every entity appeared but there was no data displayed (e.g. "Battery 1 SoC: Unknown") and after a view minutes I got an error:

Error connecting to inverter (friendly name: ""). Error reading registers. Type: RegisterType.HOLDING; start: 31000; count: 91; slave: 247 from tcp://192.168.1.xxx:502: Modbus Error: [Input/Output] Modbus Error: [Invalid Message] No response received, expected at least 8 bytes (0 received)

This might be a problem to adress in a homeassistant forum but I wanted to share it anyway since it might also be an issue on the inverters side that stops the sharing of information.

EDIT2:

I fixed the problem. Since I can see all the entities (including the controllable ones like "work mode") I tried to play with some of them during the state of "Connected" (it was always in this state for about 1min when I changed the integrations version or just pressed "Reload" in the integrations options). Changing "Work mode" to "Self use" (which the inverter was already in) fixed the issue and now all the data is where it should be. I hope it helps someone out there. Took me just about 14 hours...
Re: H3-12.0-Smart Modbus Connection
Hi, just reading through this - am I correct that you've got it connected and working without having to connect your own modbus?

I've just got the H3-15.0-Smart installed.
Thanks
Re: H3-12.0-Smart Modbus Connection
That is correct. I actually did this while being not at home at all ;). No additionally device has been connected to the inverter. The only thing I needed someone at home to check was the inverters slave ID but no change was needed since the slave ID was already at 247.
Re: H3-12.0-Smart Modbus Connection
Thanks. Got my data coming through now. The only thing missing is the cumulative generation from my AC coupled solar. We'll do some digging to see if that's available somewhere.
Re: H3-12.0-Smart Modbus Connection
Dave Foster wrote: Fri Aug 29, 2025 9:22 am No that's where the datalogger plugs in and Fox have un-helpfully labelled it the COMM/Dongle port

This is the COM port

111.jpg

And these are the pin outs for it.

222.jpg
Hallo gibt es für den Stecker eine genaue Bezeichnung? Hast du vielleicht auch ein Amazon Link? Dankeschön
Re: H3-12.0-Smart Modbus Connection
smarthomie wrote: Sat Jan 31, 2026 1:13 pm That is correct. I actually did this while being not at home at all ;). No additionally device has been connected to the inverter. The only thing I needed someone at home to check was the inverters slave ID but no change was needed since the slave ID was already at 247.
I am currently trying to set this up for my H3-10.0 Smart Inverter without success. When i start the integration it shows "Connected" and the entities are created, but after round about 1 minute it shows the same message you mentioned above:

Connection Status changed to Error reading registers. Type: RegisterType.HOLDING; start: 31000; count: 91; slave: 247 from tcp://192.168.0.xxx:502: Modbus Error: [Input/Output] Modbus Error: [Invalid Message] No response received, expected at least 8 bytes (0 received)

Even if I try to change the Work mode while the Inverter is connected it shows the following message:

The Action select/select_option konnte nicht ausgeführt werden. Error writing registers. Start: 41000; values: [2]; slave: 247 from tcp://192.168.0.xxx:502: Modbus Error: [Input/Output] No Response received from the remote slave/Unable to decode response

The Device ID is set to 247 in Settings > Communication > Modbus TCP

Anything else i need to set up?

Which Master / Slave Version you are currently using?

Thank you.
User avatar
Site Admin
Re: H3-12.0-Smart Modbus Connection
Tschakko wrote: Tue Mar 03, 2026 8:59 pm
smarthomie wrote: Sat Jan 31, 2026 1:13 pm That is correct. I actually did this while being not at home at all ;). No additionally device has been connected to the inverter. The only thing I needed someone at home to check was the inverters slave ID but no change was needed since the slave ID was already at 247.
I am currently trying to set this up for my H3-10.0 Smart Inverter without success. When i start the integration it shows "Connected" and the entities are created, but after round about 1 minute it shows the same message you mentioned above:

Connection Status changed to Error reading registers. Type: RegisterType.HOLDING; start: 31000; count: 91; slave: 247 from tcp://192.168.0.xxx:502: Modbus Error: [Input/Output] Modbus Error: [Invalid Message] No response received, expected at least 8 bytes (0 received)

Even if I try to change the Work mode while the Inverter is connected it shows the following message:

The Action select/select_option konnte nicht ausgeführt werden. Error writing registers. Start: 41000; values: [2]; slave: 247 from tcp://192.168.0.xxx:502: Modbus Error: [Input/Output] No Response received from the remote slave/Unable to decode response

The Device ID is set to 247 in Settings > Communication > Modbus TCP

Anything else i need to set up?

Which Master / Slave Version you are currently using?

Thank you.
Make sure you're on the latest inverter firmware and make sure you have the home assistant integration set to the beta branch and restart home assistant.
Community Admin / FoxESS Elite Professional

Image Did I help you? Feel free to leave me a tip
Image Book a zoom meeting for remote consultancy or help
Image Switch to Octopus and earn £50
Image Subscribe to my YouTube channel

3 x KH Hybird Inverters (Parallel Mode)
1 x H1 Gen1 (Solar Mode)
1 x H1 Gen2 WL (Testing, Modbus and API development)
24 x HV2600 (62.4kWh), 2 x EP12, 2 x ECS2900
32 x 490w across 4 arrays

2 x EV's (Tesla & Mercedes) Fox ESS EV Charger & Hypervolt Chargers
Heatpump & Low Carbon Housebuild
Re: H3-12.0-Smart Modbus Connection
Hi everybody,

We've also got a H3-10.0smart Inverter with battery and I want to connect to it from Home Assistant using the Fox ESS Modbus Integration. I already located the right IP and it has port 502 open. But when I try to connect to it it shows "Exception Response (131, 3, Illegal Address)" (which also is better than no connection I guess).
Firmware up to date (Inverter Master 1.39, Slave 1.00, Manager 1.24, AFCI 0.35; WLAN-Logger 2.03; Battery 2.004).
The HA FoxESS Integration is the latest on the beta branch. HA has restarted several times no without change.

Do you have any suggestions what I can try?