Hi
Could anyone advise as to the settings for the above in order to setup for export limitation ? I can fin info for the 3 phase but not single .
Also can you feed 2 inverters into one meter ?
Many Thanks
Chint DDSU666 Settings
-
- Posts: 1294
- Joined: Thu Oct 13, 2022 7:21 pm
Once the Chint is installed you set the export limit in the inverter settings (not the meter), this setting is consistent even if you are using a CT clamp rather than a meter.
One meter can only be used by a single inverter, unless the 2 inverters are capable of running in parallel mode such as the K series of H1(G2) in which case you only need one meter (or CT) and they share the meter information between them over their parallel bus.
One meter can only be used by a single inverter, unless the 2 inverters are capable of running in parallel mode such as the K series of H1(G2) in which case you only need one meter (or CT) and they share the meter information between them over their parallel bus.