I'm seeing a charge command that the inverter acknowledges but does not act on, and it seems to depend on the Min SoC (On Grid) setting. Is this expected behaviour, and is it documented anywhere?
Setup
- Homeassistant with https://evcc.io/en/ and https://github.com/nathanmarlor/foxess_modbus
- FoxESS H3-Pro-15.0, Master 2.09 / Slave 1.06 / ARM 2.06
- ECS2900-H7 battery, 20.16 kWh, Firmware 2.017 / Batteries 1.15
- evcc 0.319.1 controls the battery over Modbus TCP (unit ID 247). foxess-modbus 1.16.0 only reads.
- Min SoC 10%, Min SoC (on-grid) 20%, Max SoC 100%, work mode Self Use before the charge
Problem
When evcc starts a grid charge with the SoC BELOW Min SoC (On Grid), every write is acknowledged (no exception), the work mode reads back as Back-up, but the battery stays at 0 W. With the SoC at or above Min SoC (On Grid), the identical commands charge at about 8 kW. (Matches my settings in evcc)
Results
Code: Select all
Date/time SoC Min SoC (On Grid) Result
13 Nov 05:45 33% 20 charged (33 -> 63%)*
17 Nov 05:00 17-18% 20 no charge, battery 0 W
17 Nov 14:15 21% 20 charged, about -8.1 kW, SoC 21 -> 44% in 45 min
18 Nov 05:00 29% 30 no charge, battery 0 W
(*) 13 Nov: evcc log only, no Modbus trace. On 11 and 12 Nov it also failed at 17-19% with min 20, no trace either.
Commands (sent every 15 s, Modbus TCP, unit 0xF7)
As I read the registers: 49203 = work mode (3 = Back-up), 46002 = remote control timeout (60 s), 46607 = max charge current (0.1 A units, 500 = 50 A), 46001 = remote control enable, 46003-46004 = active power (int32, -8000 W).
Failed run, 18 Nov 05:00:06, SoC 29%, Min SoC (On Grid) 30. Frames as logged (MBAP header, unit f7, function, data):
Code: Select all
send 07 6c 00 00 00 06 f7 06 c0 33 00 03 FC06 49203 = 3
recv 07 6c 00 00 00 06 f7 06 c0 33 00 03
send 07 6d 00 00 00 06 f7 06 b3 b2 00 3c FC06 46002 = 60
recv 07 6d 00 00 00 06 f7 06 b3 b2 00 3c
send 07 6e 00 00 00 06 f7 06 b6 0f 01 f4 FC06 46607 = 500
recv 07 6e 00 00 00 06 f7 06 b6 0f 01 f4
send 07 6f 00 00 00 06 f7 06 b3 b1 00 01 FC06 46001 = 1
recv 07 6f 00 00 00 06 f7 06 b3 b1 00 01
send 07 70 00 00 00 0b f7 10 b3 b3 00 02 04 ff ff e0 c0 FC16 46003-46004 = -8000
recv 07 70 00 00 00 06 f7 10 b3 b3 00 02
Reads during the runs
Code: Select all
Failed (18 Nov 05:00:05, polled every 30 s through the whole window):
send 07 67 00 00 00 06 f7 03 99 45 00 02 read 39237 x2 (battery power, int32)
recv 07 67 00 00 00 07 f7 03 04 00 00 00 00 -> 0 W
send 07 6a 00 00 00 06 f7 03 92 ec 00 01 read 37612 (SoC)
recv 07 6a 00 00 00 05 f7 03 02 00 1d -> 29%
Successful (17 Nov 14:32:25):
recv 44 4b 00 00 00 07 f7 03 04 ff ff e0 24 -> -8156 W (charging)
recv 44 4e 00 00 00 05 f7 03 02 00 1b -> 27%
BMS block (37609, 24 regs)
My reading by position: battery temperature about 23 C in all cases, cell voltages about 3.28-3.35 V, current 0 A in the failed windows and about 19 A during the working charge.
Questions
1. Is a remote-control force charge meant to be refused when SoC is below Min SoC (On Grid)? Is this documented?
2. Is there a register that shows why the setpoint is ignored (status, limit or flag)?
3. Does anyone else see this on an H3-Pro or H3 Smart, and on which firmware?
4. A user with an H1 reported that setting Min SoC (On Grid) below the current SoC made charging resume. I haven't verified that on the H3-Pro yet.
Thanks!