Why is my battery discharging to the grid when the SoC is only 32%?
Panels are generating 3.2kW but 1.79kW are being exported to the grid?
Re: Unwanted discharge to Grid
Posted: Wed Mar 25, 2026 9:28 am
by MaterialBarracuda48
Morning,
The image shown is a snapshot of a point in time, like a picture. So the values shown could have been temporary, and the next 5 minute refresh of the data it could have stopped exporting.
That being said, it maybe your battery is a little cold and cannot take the full charge speed, more so if it fitted externally.
Can you find out your temperature of your battery and report back.
Re: Unwanted discharge to Grid
Posted: Wed Mar 25, 2026 9:51 am
by gxaxrxy2025
Hi, I have put together the chart below, not sure which line is the most important
Re: Unwanted discharge to Grid
Posted: Wed Mar 25, 2026 9:59 am
by MaterialBarracuda48
The green cellTemperatureLow controls your charge/discharge rates.
There is a chart here in the video at 5m 30s
Has your charging/export changed now a few minutes has passed?
Re: Unwanted discharge to Grid
Posted: Wed Mar 25, 2026 10:10 am
by gxaxrxy2025
It does seem to have stopped exporting but the panels have also dropped production due to the weather
Re: Unwanted discharge to Grid
Posted: Wed Mar 25, 2026 10:17 am
by MaterialBarracuda48
Today isn't the best day for checking this, but I can say for certain that it won't charge the best at the low temperature it currently is sat at.