I’m looking for some technical confirmation (or correction) from the community on two installation topics related to a Fox ESS hybrid system. I’m not trying to criticize an installer — just trying to understand the correct and intended way these systems are meant to be wired and operated.
System overview
- Fox ESS 3-phase hybrid inverter
- HV battery (11 kWh)
- Whole-home EPS (no dedicated EPS sub-panel)
- Manual 1-0-2 transfer switch (3P+N) at the main panel
- Loads are manually managed during outages (intentional)
Design intent:
A manual whole-home EPS solution where:
- The inverter automatically enters EPS on grid loss
- The 1-0-2 switch only selects the house supply source (Grid / Off / EPS)
- Circuit breakers are used for protection/service only, not as operational switches
- No manual switching is required in remote locations (e.g. garage) during an outage
In the installed setup, both the inverter AC-IN (grid) and EPS output were routed through a garage sub-panel. This resulted in:
- Additional breakers in the garage being used as operational isolation switches
- A required manual sequence (turn breaker A off, breaker B on, then flip 1-0-2) to avoid unintended backfeed
- Operational complexity and dependency on garage access during outages
- AC-IN (grid) permanently connected to the inverter (grid reference)
- EPS output routed directly from the inverter to the 1-0-2 switch and then to the main panel
- No inverter or EPS paths routed through the garage sub-panel
- Garage feed remains independent of inverter operation
From a Fox ESS best-practice point of view, is this proposed topology the correct way to implement a manual whole-home EPS system?
In other words:
- Should the inverter + transfer switch alone be sufficient for safe EPS operation when wired correctly?
- Are additional operational isolation breakers normally required, or are they a workaround for an incorrect topology?
The PV array with 10 panels is currently wired as one series string, which is then split with a Y-connector into PV1 and PV2 on the inverter.
This raises two concerns:
- Both MPPT inputs are effectively fed by the same string
- The inverter appears to “see” half the current per input, raising questions about:
- current limiting
- MPPT behavior
- whether any real benefit is gained vs using a single MPPT input
Is splitting a single PV string into PV1 & PV2 using a Y-connector:
- supported by Fox ESS, and
- electrically neutral in terms of total power/current?
- reduced current per MPPT,
- sub-optimal tracking, or
- unnecessary complexity compared to using a single PV input?
Thanks in advance for any insight or experience you can share.