During force charge, if the Max SoC is reached the PV output reduces to zero until the end of the period.
Similarly, during force discharge, if the forced discharge cutoff SoC is reached, the PV output is zero until the end of the period. In both cases any available PV is not being sent to the house load and/or grid. This is particularly bad during force charge becasue you will start using grid power for your load instead of the PV. Is there anyway to prevent this behaviour?
Also is it possible to set a level during force discharge which will not start unless the SoC is above a certain level. That way I can make sure by limiting the force discharge power that the cutoff SoC is never reached?

Re: PV during Force Charge and Force Discharge

Posted: Thu Jan 15, 2026 8:59 am
by MaterialBarracuda48
That might be caused by a duff firmware that is causing it to behave this way.

I cannot recall your other threads if you have ever had FW upgrades done, I think you are having trouble I think getting responses from Fox support IIRC.

Re: PV during Force Charge and Force Discharge

Posted: Fri Jan 16, 2026 11:32 pm
by brunofabre
I have the latest FW Master(1.58)/Slave(1.02)/Manager(1.58).
Here is the screenshots of the behaviour during Force Charge from Grid.
(1) 11:35AM - At the begining of the force charge period battery Soc is low (49%) and charging from PV(3.15kW)+Grid(7.85kw) at maximumn of 11kW.
(2) 1:29PM - Approaching the battery being fully charged (96%), the charging from PV(3.58kW)+Grid(6.12kW) is slowed slightly to 10.7kW.
(3) 1:52PM - Battery is fully charged (100%), PV(0kW) is stopped and Battery (100%) is stopped. Load(1.8kW) is from the Grid(1.8kW).
(4) 2:12PM - After the force charge period, in the default Self Use mode, PV(3.89kW) is active again and providing the Load(1.73kW), and excess is going back to the Grid(2.17kW).

Obviously there was around 3.5kW of PV during the force charge period when the battery was full (3), but the inverter stopped using it.

Is there any way to use the available PV during a force charge period when the battery is 100%.

Re: PV during Force Charge and Force Discharge

Posted: Sat Jan 17, 2026 3:30 am
by brunofabre
I changed to the basic charging with charge from grid on, and it behaves the way I want.
Screenshot_2026-01-17-13-53-40-607_com.fox.foxapp.two.jpg
Why can't the force charging from Mode Sceduler work this way?

I'm actually more interested in force discharge, which is only available in Mode Scheduler, behaving the same way. When it reaches the Forced Discharge Cutoff SoC, it should stop discharging but allow the PV to be used for house load and excess to feed into the Grid.

Re: PV during Force Charge and Force Discharge

Posted: Sat Jan 17, 2026 9:54 am
by MaterialBarracuda48
Thank you for posting in greater detail, very helpful.

I am on the same FW as yourself, but I have my charge set for cheap overnight rate that ends at 05:30 when there is currently no solar in the UK. So I cannot check the behaviour.

There maybe some bugs in the new FW's that are stopping things, or the FW is behaving as Fox intend it to. I posted here just a few moments ago, basically saying that they might need to use Home Assistant to take over the system logic and control the Inverter using the logic WE set.

I won't repeat the text, but look here please.
viewtopic.php?p=12379#p12379

Re: PV during Force Charge and Force Discharge

Posted: Sun Jan 18, 2026 10:06 pm
by brunofabre
Tried Mode Scheduler with Force Charge again and same result. When battery reaches 100% it cuts the PV power to 0W and uses the grid to power the home load.

Then switched back to basic scheduler and it didn't cut the PV when battery was at 100%. PV was used for the home load and any excess went back into the grid. This is exactly what I want, but I also want to use Force Discharge during other times, which is not available in the basic scheduler.

It seems like during force charge with the mode scheduler, during the entire period the PV can only be used to charge the battery. If during the period it reaches the FC Cutoff SOC, it cuts hte PV to 0W as it cannot charge the battery anymore.

I'm guessing if you had 15kW of PV with the KH10, which has a maximum battery charge power of 10500W, if you were force charging with the mode scheduler in full sunlight, it would cut the PV to 10500W during the period and then 0W when the battery reached the FC Cutoff SOC. I don't understand the logic of this. It should prioritize the PV to the battery rather than only exclusively to the battery.

Is there any documentation which explains in detail each of the modes, for both basic and mode scheduler, in detail so we know when to use which mode to suit our needs?

Re: PV during Force Charge and Force Discharge

Posted: Mon Jan 19, 2026 9:58 am
by MaterialBarracuda48
You are going to have to either use less Force Charge time, and then swap to Self-use to let the solar top up the rest of your battery in your scheduler, so that PV can then be used for house loads.

If not, then bite the bullet and go all in with Modbus & Home Assistant for full control.

Re: PV during Force Charge and Force Discharge

Posted: Mon Jan 19, 2026 10:25 pm
by brunofabre
Thanks for trying to help but for me the best thing is to use the basic force charge with charge from grid enabled. It behaves the way I want.
Dave has replied in another post that the mode scheduler behaviour I'm experience was a bug introduced in a recent fw release. I'll wait until that is fixed until I switch back to mode scheduler and look into using force discharge.

Re: PV during Force Charge and Force Discharge

Posted: Tue Jan 20, 2026 8:55 am
by MaterialBarracuda48
Oh for sure, whatever works best for you own use case scenario.
The system is not behaving as expected for a few people, and like most FW upgrades, fix one thing and break another.

Re: PV during Force Charge and Force Discharge

Posted: Tue Mar 03, 2026 6:24 pm
by BigNickUK
I have just noticed this on the app, we had our forced discharge in the evening capped at 60% SOC so that we could revert to battery power for the evening.
Its utterly pointless discharging if during that period you are powered from the grid at premium rate.
I dont recall this happening before prior to the new updates

Re: PV during Force Charge and Force Discharge

Posted: Wed Apr 15, 2026 3:41 pm
by TEDengservices
Hi I am curious about this because I have the same problem. However my battery isn't 100% and my PV sits at zero. Its close to 100% but isn't. I miss out on export and actually draw from the grid. Always at 13:30 when mode scheduler starts a force charge. I have had the system for around 2 yrs and it has never previously done this. I am sick of Fox now. They have updated the app and things stopped working then they updated the inverter and the mode scheduler wouldn't save. It seems to have behaved for the last 3 months but now I notice its doing this PV cut off during force charges. Its literally costing me money now. I am really starting to get sick of Fox's dodgy software updates.

Re: PV during Force Charge and Force Discharge

Posted: Mon May 18, 2026 2:13 pm
by cjau
I noticed a similar thing, that when I had forced charge or discharge, once it reached the limit it stayed in the mode and did not charge or discharge the battery further. I had thought it might revert to Self-Use mode, but it doesn't. So I had to manually monitor to change back to Self-Use or turn off it I didn't want it happening. I guess it wants to maintain the battery at the specified limit, so it won't charge or discharge further.

In my situation PV wasn't a problem because it was during the night (exporting at peak time or charging at cheap night-time rate). The charging at cheap rate wasn't so bad, as buying extra cheaper electricity was ok. However, I didn't want it to stop discharging in peak hour and instead I buy at peak prices, when I still had charge in my battery. That would undo my export for profit.

While I'm at it, I would also have liked the scheduler to have day of week options not just time, as I have some different weekend rates. I guess I need to checkout Home Assist...

Re: PV during Force Charge and Force Discharge

Posted: Wed May 20, 2026 10:16 am
by JEFFERSON53
Apologies if I've posted this in the wrong place but my limited knowledge lets me think you are all talking around a similar problem I have.
I had a new in PV system with battery installed last June. We are an all electric house (apart form the wood burners) and use Night Storage Heaters charged from cheaper Off Peak electricity. After discussion with my installer in October he made changes to my FOXCloud settings so that my battery would be topped up during the night (1am to 5am) so that in the morning we have a full battery should it not be a productive PV day and have to use peak rate electricity.
In the interim period FOX Cloud app has changed and I do not recognise any of the settings to change back to the summer settings of requiring no overnight top up.
The current setting I see on the App is NORMAL / SELF USE
Can anyone guide me please to how to change the settings, TIA

Re: PV during Force Charge and Force Discharge

Posted: Wed May 20, 2026 2:45 pm
by cjau
JEFFERSON53 wrote: ↑Wed May 20, 2026 10:16 am Apologies if I've posted this in the wrong place but my limited knowledge lets me think you are all talking around a similar problem I have.
I had a new in PV system with battery installed last June. We are an all electric house (apart form the wood burners) and use Night Storage Heaters charged from cheaper Off Peak electricity. After discussion with my installer in October he made changes to my FOXCloud settings so that my battery would be topped up during the night (1am to 5am) so that in the morning we have a full battery should it not be a productive PV day and have to use peak rate electricity.
In the interim period FOX Cloud app has changed and I do not recognise any of the settings to change back to the summer settings of requiring no overnight top up.
The current setting I see on the App is NORMAL / SELF USE
Can anyone guide me please to how to change the settings, TIA
I'm fairly new to all this too, but if it is the same as mine, then you will have Work Mode set to Mode Scheduler. When I schedule is not in operation then it will default to Self-Use (which is what you probably want normally). If you click on that and edit the schedule you can disable the current schedule so it isn't used. Don't delete it just disable it. Then whenever you want it again you can enable again.
mode-scheduler.PNG
mode-scheduler.PNG (98.29 KiB) Viewed 25318 times

Re: PV during Force Charge and Force Discharge

Posted: Mon May 25, 2026 12:53 pm
by diarmidr
My FoxESS app has updated in the last few days, and along with a slight change to how "force charge" is defined, this issue seems to have been resolved.

I just tested it setting Force Charge with a max SOC of 30% for 12:30-13:00. From starting SOC of 15% it charged my EP6 using the ~500W PV output and the max possible grid import of 3.7kW. After 15 minutes it hit 30% SOC, where it stopped grid importing and only charged the battery from PV. Thanks Fox for fixing this important bug!

My only remaining complaint is that I'd like to be able to cap the battery charging power so that I could reduce the average temperature of the battery and extend its life.

Re: PV during Force Charge and Force Discharge

Posted: Tue May 26, 2026 10:47 am
by JEFFERSON53
cjau wrote: ↑Wed May 20, 2026 2:45 pm
JEFFERSON53 wrote: ↑Wed May 20, 2026 10:16 am Apologies if I've posted this in the wrong place but my limited knowledge lets me think you are all talking around a similar problem I have.
I had a new in PV system with battery installed last June. We are an all electric house (apart form the wood burners) and use Night Storage Heaters charged from cheaper Off Peak electricity. After discussion with my installer in October he made changes to my FOXCloud settings so that my battery would be topped up during the night (1am to 5am) so that in the morning we have a full battery should it not be a productive PV day and have to use peak rate electricity.
In the interim period FOX Cloud app has changed and I do not recognise any of the settings to change back to the summer settings of requiring no overnight top up.
The current setting I see on the App is NORMAL / SELF USE
Can anyone guide me please to how to change the settings, TIA
I'm fairly new to all this too, but if it is the same as mine, then you will have Work Mode set to Mode Scheduler. When I schedule is not in operation then it will default to Self-Use (which is what you probably want normally). If you click on that and edit the schedule you can disable the current schedule so it isn't used. Don't delete it just disable it. Then whenever you want it again you can enable again.

mode-scheduler.PNG
Thank you for that guidance and this appears to have solved my issue - Cheers

Re: PV during Force Charge and Force Discharge

Posted: Wed May 27, 2026 10:31 am
by diarmidr
diarmidr wrote: ↑Mon May 25, 2026 12:53 pm My FoxESS app has updated in the last few days, and along with a slight change to how "force charge" is defined, this issue seems to have been resolved.

I just tested it setting Force Charge with a max SOC of 30% for 12:30-13:00. From starting SOC of 15% it charged my EP6 using the ~500W PV output and the max possible grid import of 3.7kW. After 15 minutes it hit 30% SOC, where it stopped grid importing and only charged the battery from PV. Thanks Fox for fixing this important bug!

My only remaining complaint is that I'd like to be able to cap the battery charging power so that I could reduce the average temperature of the battery and extend its life.
Actually I don't think it was fixed - have tested this again and it's still giving the problem where PV output is limited to the power the battery is charging at.

Re: PV during Force Charge and Force Discharge

Posted: Wed Jun 03, 2026 9:47 am
by diarmidr
My issues with force charge and solar output appear to have been fixed by upgrading to latest firmware.
Inverter model H1-3.7-E-G2-Wl

Firmware:
Master: 1.53
Slave: 1.04
Manager: 1.39