As I understand it, reading data from the inverter (H1 in my case) is a spot reading not "cumulative since the last reading"... Hmm, now I actually write it down, I suppose it would have to be, but I'll ask the question anyway. Is that right? I'm specifically thinking of power here, generated and exported.
Is there a way to get cumulative data? If it's "turn up the frequency of collecting readings" (I use Home Assistant and the ModBus extension), any suggestions how far that needs to go to a) get a good approximation and b) not save vast amounts of data.
This has been prompted (this time) because Octopus are telling me that in the month to 19 of June we only exported just over half of what we did in the previous month, which seems a bit unlikely given the weather we've had. Anyone else seen this?
They show up in both in the app, and also modbus, for me.
Sensors
Ambient Temp 42.0 °C
Battery Charge 0.00 kW
Battery Charge Today 11.00 kWh
Battery Charge Total 2,732.40 kWh
Battery Discharge 1.44 kW
Battery Discharge Today 11.60 kWh
Battery Discharge Total 2,825.50 kWh
Battery SoC 20%
Battery SoH 100%
Battery Temp 35.5 °C
BMS Cell mV High 32 mV
BMS Cell mV Low 32 mV
BMS Cell Temp High 33.2 °C
BMS Cell Temp Low 28.9 °C
BMS Charge Rate 50.00 A
BMS Discharge Rate 50.00 A
BMS kWh Remaining 16.58 kWh
Connection Status Connected
CT2 Meter -0.00 kW
Feed-in 0.00 kW
Feed-in Today 27.600 kWh
Feed-in Total 4,396.800 kWh
Grid Consumption 0.01 kW
Grid Consumption Today 17.00 kWh
Grid Consumption Total 3,061.80 kWh
Grid CT -0.01 kW
Grid Frequency 50 Hz
Grid Voltage 249 V
Input Energy Today 11.30 kWh
Input Energy Total 2,779.00 kWh
Inverter Battery Current 6.20 A
Inverter Battery Power 1.4420 kW
Inverter Battery Voltage 232 V
Inverter Current 5.30 A
Inverter Fault Code None
Inverter Power 1.37 kW
Inverter State On Grid
Inverter Temp 33.5 °C
Load Energy Today 15.70 kWh
Load Energy Total 1,412.80 kWh
Load Power 1.38 kW
Max Charge Current 50.00 A
Max Discharge Current 50.00 A
Max SoC 100%
Min SoC 10%
Min SoC (On Grid) 10%
PV Power 0.00 kW
PV1 Current 0.00 A
PV1 Power 0.00 kW
PV1 Power Total 0.000 kWh
PV1 Voltage 0 V
PV2 Current 0.00 A
PV2 Power 0.00 kW
PV2 Power Total 1,576.512 kWh
PV2 Voltage 0 V
PV3 Current 0.00 A
PV3 Power 0.00 kW
PV3 Power Total 1,817.191 kWh
PV3 Voltage 3 V
PV4 Current 0.00 A
PV4 Power 0.00 kW
PV4 Power Total 0.029 kWh
PV4 Voltage 0 V
Solar Generation Today 30.40 kWh
Solar Generation Total 3,400.40 kWh
Version: Manager 1.37
Version: Master 1.41
Version: Slave 1.01
Yield Today 37.90 kWh
Yield Total 5,554.90 kWh
Hmm, yes, of course they do.
Sorry, my bad. Thanks for pointing that out.