N-E Grounding & Backup Generator starting

Post Reply
Kris
Posts: 7
Joined: Tue Feb 14, 2023 6:19 pm

Hello all, I am trying to resolve a floating neutral problem when running off-grid, (H1AC1 6kw Inverter and 18kw of HV2600 batteries) I thought that the H1-AC1 had an internal N-E Bonding Relay, (Grounding setting?) but when I disconnect from the grid, I am getting a reading if 100v between N and E, and RCDs wouldn't operate, Do I need to install an external N-E bonding relay?

Also, I am looking at total grid disconnection and installing a backup generator for days when the batteries don';t get enough charge of the solar, is there a way to start the Generator and close the contactor when Batterues reach a certain SOC, and then open contactor and switch of genny when SOC reaches 95%?
I have a dedicated Home assistant system running from a raspberry PI connected to inverter, and wondered if I could trigger from this.

Many thanks

Kris
User avatar
Will
Site Admin
Posts: 250
Joined: Thu Oct 13, 2022 5:56 pm

I believe you need an earth spike connected to the P+E of the EPS plug for this to work.
Community Admin / FoxESS Professional

Buy me a coffee or Book a zoom meeting for remote consultancy

FoxESS Tri Inverter Installation
2 x KH Series Inverters
24 x HV2600 (62.4kWh)
32 x 490w across 4 arrays
Dual Tesla Household
Heatpump & Low Carbon Housebuild