V1 and V2

Posted: Tue Nov 22, 2022 11:17 am
by Foxy
Looking on the info panel of my Fox inverter I can see readings under the solar menu as of now as

V1 is showing 371.3 v
I1 is showing + 2.3 a
P1 is showing + 875w

V2 is showing 2.0 v
I2 is showing 0.0 a
P2 is showing 0w

I have 12 panels presumably split into two. Does the above reading say I have a problem with 1 set?
Can anyone advise
Thanks

Re: V1 and V2

Posted: Wed Nov 23, 2022 9:30 pm
by Dave Foster
At this time of year, the 371V sounds about right for the voltage you would expect for 12 panels - that suggests you’ve got one string of 12 and that they haven’t been split as you might expect. At maximum voltage it still falls within the 600v limit of a Fox inverter, but you’d need to check on the specs of the panels to make sure they are not exceeding the current limits.

Re: V1 and V2

Posted: Thu Nov 24, 2022 8:49 pm
by Foxy
Hi Dave
Many thanks for the information

Re: V1 and V2

Posted: Mon Nov 28, 2022 11:57 am
by Will
Do you mean PV1 and PV2 not v1 / v2?