FOX ESS Hybrid H1 5KW - Grid sending to Load when not needed???

Posted: Tue Oct 31, 2023 10:08 am
by vasco.gouveia
Hi Everyone

I've got an issue with my Hybrid Inverter, when it's producing around 1800W, it's also drawing the same amount from the GRID???
The more I'm producing on the PV, and sends it to the LOAD, it also gives me the indication that the grid is inputting the same amount??

PV 2.979KW
Hybrid AC 2.928 KW - No batteries connected to them - since I want to use it with Inverter option only, at least for now.
Load 5.672KW
Grid 2.742KW

Is there something I need to look at?

Re: FOX ESS Hybrid H1 5KW - Grid sending to Load when not needed???

Posted: Tue Oct 31, 2023 12:41 pm
by calum
Does the load look accurate to you? If the available solar power is not enough for the load, it will draw from the grid to fulfil the rest.

Re: FOX ESS Hybrid H1 5KW - Grid sending to Load when not needed???

Posted: Tue Oct 31, 2023 7:37 pm
by Dave Foster
We could really do with a screen shot of your real time data screen (app) or the energy flow (on the website) - that will help show what you are describing - is it a new installation? as it sounds like the CT clamp is not reading the load correctly.