Page 1 of 1

DNO will not allow 23kWp export

Posted: Mon Nov 23, 2026 8:50 am
by MattC
Hello,

I have a recently installed 45 panel domestic system capable of a potential 23kWp production. This is about 5 times the power consumption. I do not (yet) have either an electric car nor an air-source heat pump.Therefore at the moment I do not need battery storage.

My problem is that my DNO has throttled my export back to 10.5kW.

I guess that I have a couple of questions.

Firstly, is the 10.5kW limit a peak figure or an average over (say) 24 hours?

Secondly, what would be the potential cost benefit analysis of getting 3-phase?

Thirdly, has anyone else had this issue and, if so, how did you resolve it?

Many thanks in advance.

Kind regards,

Matt

Re: DNO will not allow 23kWp export

Posted: Mon Nov 23, 2026 7:23 pm
by Dave Foster
No it isn’t an average, it is the maximum instantaneous power output and you must not exceed that.

Having batteries would allow you to store any excess and either use it yourself, or feed it back as export later when the sun isn’t shining and the export tariff may be higher.

In all honesty 10.5kW is quite a good single phase limit the DNO has allowed you, it’s more often to see 7kW or less.

Going 3 phase would allow you to split the output over each phase, so a G98 would allow 3.68kW * 3, but you would need to check with your DNO what the limitations of the locale are, you may not easily be able to move to a 3 phase system, and the cabling and switchgear costs would be significant; it’s hard to see how any cost/benefit would work out in your favour.