Force charge not working when drifting below MinSoc? (H3 Pro)

Posted: Wed Nov 18, 2026 9:59 am
by gameovernl
Hi all,

I'm seeing a charge command that the inverter acknowledges but does not act on, and it seems to depend on the Min SoC (On Grid) setting. Is this expected behaviour, and is it documented anywhere?

Setup
- Homeassistant with https://evcc.io/en/ and https://github.com/nathanmarlor/foxess_modbus
- FoxESS H3-Pro-15.0, Master 2.09 / Slave 1.06 / ARM 2.06
- ECS2900-H7 battery, 20.16 kWh, Firmware 2.017 / Batteries 1.15
- evcc 0.319.1 controls the battery over Modbus TCP (unit ID 247). foxess-modbus 1.16.0 only reads.
- Min SoC 10%, Min SoC (on-grid) 20%, Max SoC 100%, work mode Self Use before the charge

Problem
When evcc starts a grid charge with the SoC BELOW Min SoC (On Grid), every write is acknowledged (no exception), the work mode reads back as Back-up, but the battery stays at 0 W. With the SoC at or above Min SoC (On Grid), the identical commands charge at about 8 kW. (Matches my settings in evcc)

Results

Code: Select all

Date/time      SoC      Min SoC (On Grid)   Result
13 Nov 05:45   33%      20                  charged (33 -> 63%)*
17 Nov 05:00   17-18%   20                  no charge, battery 0 W
17 Nov 14:15   21%      20                  charged, about -8.1 kW, SoC 21 -> 44% in 45 min
18 Nov 05:00   29%      30                  no charge, battery 0 W
(*) 13 Nov: evcc log only, no Modbus trace. On 11 and 12 Nov it also failed at 17-19% with min 20, no trace either.
Also on 17 Nov afternoon the battery charged normally from PV while the SoC was 18-19%, below the minimum, in Self Use. Only the remote-control charge is ignored.

Commands (sent every 15 s, Modbus TCP, unit 0xF7)
As I read the registers: 49203 = work mode (3 = Back-up), 46002 = remote control timeout (60 s), 46607 = max charge current (0.1 A units, 500 = 50 A), 46001 = remote control enable, 46003-46004 = active power (int32, -8000 W).

Failed run, 18 Nov 05:00:06, SoC 29%, Min SoC (On Grid) 30. Frames as logged (MBAP header, unit f7, function, data):

Code: Select all

send 07 6c 00 00 00 06 f7 06 c0 33 00 03          FC06 49203 = 3
recv 07 6c 00 00 00 06 f7 06 c0 33 00 03
send 07 6d 00 00 00 06 f7 06 b3 b2 00 3c          FC06 46002 = 60
recv 07 6d 00 00 00 06 f7 06 b3 b2 00 3c
send 07 6e 00 00 00 06 f7 06 b6 0f 01 f4          FC06 46607 = 500
recv 07 6e 00 00 00 06 f7 06 b6 0f 01 f4
send 07 6f 00 00 00 06 f7 06 b3 b1 00 01          FC06 46001 = 1
recv 07 6f 00 00 00 06 f7 06 b3 b1 00 01
send 07 70 00 00 00 0b f7 10 b3 b3 00 02 04 ff ff e0 c0     FC16 46003-46004 = -8000
recv 07 70 00 00 00 06 f7 10 b3 b3 00 02
Successful run, 17 Nov 14:15:26, SoC 21%, Min SoC (On Grid) 20: the same five writes and acknowledgements, with different transaction IDs only.

Reads during the runs

Code: Select all

Failed (18 Nov 05:00:05, polled every 30 s through the whole window):
send 07 67 00 00 00 06 f7 03 99 45 00 02     read 39237 x2 (battery power, int32)
recv 07 67 00 00 00 07 f7 03 04 00 00 00 00  -> 0 W
send 07 6a 00 00 00 06 f7 03 92 ec 00 01     read 37612 (SoC)
recv 07 6a 00 00 00 05 f7 03 02 00 1d        -> 29%

Successful (17 Nov 14:32:25):
recv 44 4b 00 00 00 07 f7 03 04 ff ff e0 24  -> -8156 W (charging)
recv 44 4e 00 00 00 05 f7 03 02 00 1b        -> 27%
Read-back of the settings on the failed run: 49203 -> 00 03 (Back-up) from 05:00:13. 46607..46611 (5 regs) -> 01 f4 01 f4 00 0a 00 64 00 1e = 500, 500, 10, 100, 30. On 17 Nov afternoon the last value was 00 14 (20).

BMS block (37609, 24 regs)
My reading by position: battery temperature about 23 C in all cases, cell voltages about 3.28-3.35 V, current 0 A in the failed windows and about 19 A during the working charge.

Questions
1. Is a remote-control force charge meant to be refused when SoC is below Min SoC (On Grid)? Is this documented?
2. Is there a register that shows why the setpoint is ignored (status, limit or flag)?
3. Does anyone else see this on an H3-Pro or H3 Smart, and on which firmware?
4. A user with an H1 reported that setting Min SoC (On Grid) below the current SoC made charging resume. I haven't verified that on the H3-Pro yet.

Thanks!

Re: Force charge not working when drifting below MinSoc? (H3 Pro)

Posted: Thu Nov 19, 2026 10:14 pm
by gameovernl
Update after further testing. :)

The charge is ignored only when the SoC is a little below "Min SoC (On Grid)" (register 46611). The exact threshold is still unknown.

What I see when I try a force charge

Code: Select all

Actual SoC vs 46611		Inverter before the charge command	Result
1-3 points below		idle, 0 W                   		command acknowledged, NO charge
12 points below			trickle charge, about -0.48 kW		charged at about -7.9 kW within 30 s
30 points below			trickle charge, about -0.47 kW		charged at about -8.1 kW within 30 s
at or above				normal								charged at about -8 kW
The 1-3 points below cases were three early-morning runs (SoC 17-18% vs MinSoC 20, 29% vs 30, 24% vs 25) and the test below (25% vs 27). The "far below" cases were done in daylight and in the dark, so time of day is not the cause.

Reproduced on demand, 19 Nov, evening, no PV, Self Use, battery idle at 0 W
- SoC 25%. 22:26:05: 46611 changed from 25 to 27 (0x001b). The inverter did not start a trickle charge.
- 22:29:54: evcc wants to starts a charge, sending every 15 s: 49203=3, 46002=60, 46607=500, 46001=1, 46003/46004=-8000 W. All writes acknowledged, no exceptions. Battery power stays at 0 W, no charging happening.
- 22:32:03: 46611 changed from 27 to 20 (0x0014), with the same commands still being sent. Battery power was -7888 W at 22:33:23.

The SoC, the commands and the time of day were identical, and only 46611 changed.

Observation
When the SoC is far below Min SoC (On Grid), the inverter charges the battery by itself in Self Use, and in that state the remote charge works. With the SoC only 1-3 points below, it neither charges by itself nor accepts the remote command. Overnight standby drift puts an idle battery in exactly that band whenever it sits at the minimum, and in my case, a force charge is not working. The commands are accepted, no errors, but no actual charging happens.

Questions: Is this intended? Does anyone know the width of that band, or whether another register shows why the setpoint is ignored? I'm working around it for now with an HA automation that lowers 46611 when the work mode switches to Back-up, and I'll report how that goes.

Re: Force charge not working when drifting below MinSoc? (H3 Pro)

Posted: Fri Nov 20, 2026 10:55 am
by gameovernl
Another update:

My workaround for forced charging worked.

As soon as homeassistant sees the work-mode switching to back-up (the signal that evcc has started it's charge command) the automation I created sets the MinSoC (on-grid) to 10% instead of the regular (currently) 25%.

Then, within a minute, the force charge is running. After evcc is done running its force charge, it resets the MinSoC (On-grid) to 25%.

So for now I have my planned forced charging working again, but I still find it strange that there is a window surrounding the MinSoC (On-grid) value, where the inverter just doesn't force charge when the actual SoC is a bit lower. Seems like a bug to me.

Re: Force charge not working when drifting below MinSoc? (H3 Pro)

Posted: Sat Nov 21, 2026 11:24 am
by gameovernl
This morning my forced charge with the workaround of setting the MinSoC at least 10 points lower than the actual SoC when the charging commands are running, worked again.

I will submit these findings to FoxESS, to see if this is an actual bug or somehow expected behaviour.