Hello, I'm still getting to know my system. I've searched this forum and videos and adjusted my settings as advised, but still have some questions. This is my setup:

5kw Fox H1 series (G2) inverter
10kw Fox EP11 battery
12 x 455kw panels
Heat Pump supplies my heating & hot water

Current tariff is Octopus Flux Import. During the 2am-5am cheap period, I force charge the battery and also heat my water tank (once daily does me fine). I also run things like a de-humidifier, dishwasher, washing machine etc (if there's no sun forecast) during this period.

QUESTION 1: Can the above be scheduled to all run consecutively at 2am, or do they need to be staggered?

QUESTION 2: There is a heater in my (externally mounted) battery - once it gets colder and starts to kick in, does this need to be turned off during the force charge period or both functions work at the same time?

QUESTION 3 : Is there a weather compensation setting in the Fox app, so that the force charge doesn't activate if the following day is likely to have plenty of sun to fill my battery?

QUESTION 4 - On cloudy days, my LX needs drain the battery by late evening, so I'm back on the grid. Given I have a HP, is this to be expected for this size battery or do I need to hunt for why its happening? I was led to believe the battery it should meet my needs. (HP is set on constant temperature 24/7 as I was told this was the most efficient. House is well insulated).

QUESTION 5: Given all the above, do you think this force charge setup on Octopus Flux Import is best for me, or should I look at switching to a different tariff that is compatible with Charge Pack?

Thanks so much in advance for any advice.
RubyRoo

Re: Force Charge questions from a newbie grateful for help

Posted: Tue Nov 17, 2026 8:20 pm
by MaterialBarracuda48
1. Everything should be able to run at the same time, average UK home runs on 80Amp incoming fuse (always a few on lower/higher of course) 80Amps x 230Volts = 18.4kW of import power. Note that you do need to have the Inverter made aware of this capacity on your supply, or it could throttle.

Press 'Quick Settings' on FoxCloud2.0 App, look for your Import value (greyed out, as you need to set via Inverter controls)
Meter_Compensation_FoxCloud20.png

2. IIRC from testing last Winter with older firmware, you could not charge AND heat at the same time, but charging actually warms up the cells quite a bit, so recommend you save the heating for later (if needed) I know from my own testing, I can pull the full power from the battery at 8°C (see image)
FoxCloud2.0 Filtered Graph.png

3. I am not aware of any settings like this, but see below, if you set a program like this (if you are joining Cosy tariff) then what it will do IRL is this... if the battery has 37% SoC at the start of 22:00 charge session, it will add 3% from grid, and stop charge. If you have above the 40% SoC for the same time, then it won't charge at all. Naturally, you might actually want to have a higher SoC, it depends on your needs.


4. During Winter, a fair few Octopus customers swap to 'Cosy' tariff as the heat pump needs do increase the demand.
Here is an example of the Cosy schedule, you are looking at 8hrs at half-price electric.
Octopus Cosy Schedule.png
Note that you can STOP the battery from discharging once it reaches the SoC you program, and use 'After charging cut-off' to set the battery to 'Standby' or 'Backup' mode to hold the charge during your cheap slot, then 'release' this power after, when in higher import costs.
Full-Sized Charge.png

5. You may have to read/think and if needed ask some more questions before you make this decision.