Can a 3 phase EPS be fitted to a single phase inverter?

Posted: Mon Nov 16, 2026 7:40 pm
by mikrt
Hi,

I have 2 x EP12s and an H1-6.0-E-G2-WL inverter.

I'm looking into getting an EPS fitted, and, for some reason, the 3 phase models (EPS 3PH) are a lot cheaper than the single phase units.

Would a 3 phase EPS be compatible?

Thanks :P

Re: Can a 3 phase EPS be fitted to a single phase inverter?

Posted: Fri Nov 20, 2026 9:45 am
by Dave Foster
The original 3 phase models are less intelligent than the later versions, the new ones have an RS485 connection from the inverter to the switch which allows automated control of switching when the grid fails, rather than electro-mechanical.

The only other thing to say is that 3 phase models will have lower rated contacts as an H3-10 is rated for 3.33kW on each phase whereas a KH10 is the full 10kW on a single phase.

Re: Can a 3 phase EPS be fitted to a single phase inverter?

Posted: Sun Nov 22, 2026 2:09 pm
by mikrt
Thank you @Dave Foster :D