Fox ESS H3-12.0-Smart: 150-190 W "lost" when Anker Solarbank 2 feeds the house at night
Posted: Mon Nov 16, 2026 10:57 am
Fox ESS H3-12.0-Smart + EK12 Plus with Anker Solix
Solarbank 2: about 150–190 W "disappear" in the
inverter – anyone seen this?
Hi everyone, I have a new Fox ESS system and cannot explain how it behaves together with my
existing Solarbank. I tried to measure carefully and hope for experiences or ideas.
1. System
• Inverter: Fox ESS H3-12.0-Smart (WR Master 1.51, Slave 1.00, Comm 1.33, AFCI 0.35), 18
modules
• Battery: Fox EK12 Plus, 11.52 kWh (Bat M 1.013, S1 1.13)
• Meter: Chint DTSU666, three-phase
• Existing: Anker Solix Solarbank 2, approx. 3.2 kWh, single-phase, schedule mode. A Hoymiles
micro-inverter is connected to a different phase.
• Fox setting during the test: discharge of the Fox battery blocked below approx. 55 % SoC (the
Fox battery was not supposed to discharge)
• Goal: keep the Solarbank as a second storage: charge by day, feed the house at night, empty by
morning.
2. Observation
When the Solarbank feeds e.g. 200 W at night, only about 45 W (base load) arrive in the house. The
remaining approx. 150–190 W cannot be found: the grid stays at about 0 net, the Fox battery does
not charge, and the Anker battery is still drained. Meanwhile the Fox display shows "Power" of about
−159 to −169 W.
3. Measurement (night test 15 Nov 2026, 21:14 to 23:16, approx. 2.03 h)
Value Start End
Solarbank setting 200 W 200 W
Anker battery 99 % 84 %
Fox battery (SoC) 56 % 55 %
Fox daily counter charge 9.3 kWh 9.3 kWh (unchanged)
Fox daily counter discharge 4.9 kWh 5.0 kWh
Chint import (Imp) 28.87 kWh 29.07 kWh (+0.20)
Chint export (Exp) 56.94 kWh 57.14 kWh (+0.20)
Grid meter (import / export) unchanged unchanged
Fox "Power" (display) approx. −159 W approx. −169 W
The Chint counts per phase: the Solarbank feeds in on one phase (Exp), the other phases draw (Imp). That is
why Imp and Exp both rise by 0.20 kWh. Only the difference Exp − Imp matters, and it is ≈ 0 Wh.
4. Energy balance
Item Value Calculation / note
Output from Anker battery approx. 480 Wh 15 % × approx. 32 Wh per % (at 3.2 kWh)
of which house base load approx. 92 Wh approx. 45 W × 2.03 h
Surplus from the Solarbank approx. 389 Wh 480 − 92
Fox charging (daily counter) 0 Wh counter unchanged
Net grid (Exp − Imp) ≈ 0 Wh 0.20 − 0.20 kWh
Unaccounted approx. 389 ≈ 190 W on average (battery side), about 165
Wh W after the Solarbank conversion losses
The 32 Wh per % for the Anker is an estimate (3.2 kWh / 100); the order of magnitude does not depend much on
it. The Fox battery was not involved: daily charge counter unchanged and SoC only −1 %.
5. Further observations
• After-run: After switching the Solarbank off (about 23:14), the Fox still showed about −160 W for
roughly 10–15 minutes although the house only needed 40–45 W. Only then did the value drop.
• Fox discharging: While the Fox battery discharged (display: battery approx. 178 W, 392 V / 0.4
A), only about 25 W arrived at the inverter output with a house load of about 45 W. Again about
150 W are missing. The FoxCloud app showed only 0.05 kW discharge at that moment, so app and
display disagree.
• PV charging in the morning (Solarbank off): MPPT sum approx. 763 W (app: "Solar" 630 W),
battery charging approx. 544 W, house approx. 69 W. About 150 W difference remain.
• Battery disconnected: After switching the battery off (BMS Lost fault, Power briefly 0, SoC "NA")
and later with the battery in standby, the Fox still showed about −154 to −156 W with the
Solarbank off.
• Temperatures: Inner 32.3 °C, inverter 21.0 °C, DSP 29.0 °C, unchanged before and after the
test. The fan never ran. So the losses do not visibly heat the inverter.
6. What I have already checked
• I consider a phase mix-up unlikely: the sum is consistent, all three phases draw, and the
independent Anker meter matches the values.
• The energy ends up neither in the Fox battery nor in the grid (counters and SoC).
• According to the datasheet (V1.5, German) self-consumption is 20 ~ 25 W, max. efficiency 97.9
%. There is no value for active operation. The observed approx. 110–190 W does not fit that.
7. My questions
• Is a self-consumption of approx. 110–190 W in active operation (battery / PV / AC mode) normal
for the H3-12.0-Smart?
• What exactly does "Power" on the display represent, and which battery value is correct (display or
app)?
• Does the Fox behave differently with an AC-coupled source (Solarbank) behind the meter, and is
there a setting for it (e.g. PQRM "Fixed PF", "MachtRateLimit")?
• Has anyone got the same combination (Fox H3 Smart + Solarbank 2) and can share experience?
Thanks for thinking along!
Note on the numbers: percentages are converted from battery readings (Anker 1 % ≈ 32 Wh, Fox 1 % ≈ 115
Wh), so they are accurate to roughly ±10 %. The Chint counters only have 0.01 kWh resolution.
1. System
modules
morning.
2. Observation
−159 to −169 W.
Value Start End
4. Energy balance
display disagree.
Solarbank off.
7. My questions
app)?