EPS cycling when EV on charge
Posted: Wed May 06, 2026 9:41 am
by Nick
Newbie here.
We have a newly installed plant with the EPS and battery storage. All works fine with Octopus Agile and a self-use mode.
Yesterday, while the EV was charging and the battery was also force-charging, we had a power outage. The EPS did its job and supported the home until the EV charger came back online and tripped the system. The EV charger stopped, and the EPS and battery powered the home until the EV charger started........repeat
Are there any particular settings that could stop this occuring? Obviously, it is not possible to predict a power cut when planning to charge the EV. The charger is a Pod-Point connected unit, and the EV load is 7kW.
Re: EPS cycling when EV on charge
Posted: Wed May 06, 2026 7:01 pm
What inverter and batteries do you have ?, suppling 7kW plus any house load is a significant load.
Most systems with EV’s are wired so that the EV is upstream of the inverter so that it doesn’t flatten your home battery.
Posted: Thu May 07, 2026 11:10 am
by Nick
Thanks for your reply.
Our system comprises
Inverter H1-5.0-E-G2-WL updated with the latest firmware
Battery EP12
FOX EPS
Both of our EV chargers are installed downstream. That answers my own question - at a max output current of 27.5A (as stated on the ID label), the 7kW load of a single EV will trip the inverter protection circuits.
Sounds like we need to get an electrician in to re-terminate the chargers upstream. The battery storage, invertor and EPS were installed as a part of the local council initiative, and I think went to the lowest bidder who has not done any more than fit and run without consideration to the household infrastructure. Frustrating.
Posted: Thu May 07, 2026 5:08 pm
Ok yep, you’ll need to move them - the H1-5 inverter has a maximum AC output of 5kW which will be your limiting factor, so the 7kW load from the EV will push it straight into overload.
It’s an easy enough job for an electrician to fit a Henley block to split the live feed just after the supply meter, one side feeding the house (and inverter) circuit, the second side feeding the EV chargers.
