H1-3.7-E inverter second string: zero current issue
Posted: Wed May 24, 2023 3:19 pm
I have a H1-3.7-E inverter. I have one string of 8 panels in series and a seperate string of 3 panels in series.
The 8 panel string works fine. The 3 panel string does not appear to work.
I have tested the panels, they are 34-35V each and individually show an expected short circuit current for sun (3-11A).
The cable between the panels and the inverter has been tested and has an expected resistance (0.4 Ohms).
Both pv1 and pv2 inputs on the inverter appear to work - as if I swap the strings around, the 8 panels continue to work as expected on pv2 - just as they do on pv1.
The PV Config setting (Setting -> Feature -> PV Config) is 'Independent'.
The inverter reports the 3 panel string as 104V (when not particularly sunny) but current is always 0.0A. (8 panel string is 250+V as more panels and current ~10A as reported by the H1 unit).
If only the 3 panel string is connected to the inverter without the 8 panel string, the inverter reports 'waiting' and does nothing (still reporting 104V, 0.0A).
The datasheet suggests the MPPT voltage range is 80-550V so I believe at 104V there should be current/generation.
Any ideas why there is no current on the 3 panel string?
Does the inverter have a 'PV start voltage setting' or equivalant? (which maybe set higher than 104V but lower than 250V?)
Thanks,
Rob
The 8 panel string works fine. The 3 panel string does not appear to work.
I have tested the panels, they are 34-35V each and individually show an expected short circuit current for sun (3-11A).
The cable between the panels and the inverter has been tested and has an expected resistance (0.4 Ohms).
Both pv1 and pv2 inputs on the inverter appear to work - as if I swap the strings around, the 8 panels continue to work as expected on pv2 - just as they do on pv1.
The PV Config setting (Setting -> Feature -> PV Config) is 'Independent'.
The inverter reports the 3 panel string as 104V (when not particularly sunny) but current is always 0.0A. (8 panel string is 250+V as more panels and current ~10A as reported by the H1 unit).
If only the 3 panel string is connected to the inverter without the 8 panel string, the inverter reports 'waiting' and does nothing (still reporting 104V, 0.0A).
The datasheet suggests the MPPT voltage range is 80-550V so I believe at 104V there should be current/generation.
Any ideas why there is no current on the 3 panel string?
Does the inverter have a 'PV start voltage setting' or equivalant? (which maybe set higher than 104V but lower than 250V?)