can you clarify to me what the DRM0 function (described in the user manual
https://www.fox-ess.com/wp-content/uplo ... Manual.pdf) does exactly? For what is it used?
Thank you.
David
Re: H3/AC3 and DRM0
Posted: Sat Sep 02, 2023 2:29 pm
by ljalves
I was wondering the same thing (different inverter, S series G2) and googling around I think it's more or less this:
(please anyone correct any mistake)
Some countries (like Australia) somehow control this modes by powerline comms and they call it DRM.
DRM = Demand Response Mode
DRM0 = DRM mode 0 (there are more modes).
Quoting some doc talking about inverters:
"[...] One of these requirements is demand response mode for zero export (DRM 0), which reduces export to grid to zero upon
command from the utility".
Putting it all together, I believe that if you enable DRM0 in the settings (and you have a CT clamp/meter connected) then when this input pin is shorted to GND the inverter will not export any power.
Re: H3/AC3 and DRM0
Posted: Sat Sep 02, 2023 5:07 pm
by ljalves
Also found:

Re: H3/AC3 and DRM0
Posted: Thu Jan 30, 2025 3:24 pm
by BikerSam86
ljalves wrote: Sat Sep 02, 2023 2:29 pm
I was wondering the same thing (different inverter, S series G2) and googling around I think it's more or less this:
(please anyone correct any mistake)
Some countries (like Australia) somehow control this modes by powerline comms and they call it DRM.
DRM = Demand Response Mode
DRM0 = DRM mode 0 (there are more modes).
Quoting some doc talking about inverters:
"[...] One of these requirements is demand response mode for zero export (DRM 0), which reduces export to grid to zero upon
command from the utility".
Putting it all together, I believe that if you enable DRM0 in the settings (and you have a CT clamp/meter connected) then when this input pin is shorted to GND the inverter will not export any power.
PIN │3 │4
Definition │DRM0 │+3.3V
Model │Socket asserted by shorting pins │ Function
DRM0 │3 4 │Operate the disconnection device.
Just to chime in, this excerpt from the manual for my H1/AC1 seems to match this with the exception of the DRM0 pin [3] being shorted with the +3.3V pin [4] (Pulled High) to trigger the export disconnect.
DRM0 Also needs enabling in my inverters menu with this:
Settings > Feature > Parm > DRM0 > Enable/Disable
I'm looking at it for Export control with my energy supply for dynamic electricity tariff pricing.
Shame I've not found a way to set the inverter charge timings outside of the website/app/API.
I would love a net-less, head-less way to manage the inverter with HomeAssistant short of connecting a microcontroller to the inverters input buttons.
I hope this is of some use to someone.