FREE Window Limitations
Posted: Fri Oct 10, 2025 3:43 am
by spammenotinoz
Hi, sorry I searched but could not find this issue discussed.
Issue: "Slow Charging Speeds" when house load is high.
Scenario:
- House has 3 phase each circuit 100A
- H3-10-Smart with EQ-4800-L9
- Free Electricity Window 11am - 2pm daily.
Issue:
Battery charges at 9.9kw fine when house load is below 10kw.
If house load is above 10kw, battery will not charge or very low speeds. CT Clamps detect Grid Load as 10kw (at 50A capacity).
I get this is likely a safety thing, but seems it should be able to be increased to 90A (still 10% below the limit of a single phase)
My installer did not know how to fix this issue, other than have high-loads by-pass the CT clamp, but then the battery cannot be used to offset their loads.
Re: FREE Window Limitations
Posted: Fri Oct 10, 2025 8:59 am
by Will
Your installer needs to speak with Fox support if they're unsure how to set the settings.
I would tell you what to change but it depends on inverter model and firmware version.
I assume they've updated you to the latest firmware and checked the common settings areas?
Posted: Fri Oct 10, 2025 11:43 am
by spammenotinoz
Will wrote: ↑Fri Oct 10, 2025 8:59 am Hello,
Thank-you for taking the time to reply. I have also raised a support call with Fox. This was the installers first FoxESS 3-phase...:)
Inverter: H3-10.0-SMART
Firmware: 1.3 (noticed it was updated last week without asking, now supports SOC of 0%, although I have left it at 10%)
Two things I noticed after this post;
- Balance Load: Disabled
- ImportLimitCurrent: 031.9A (~7kw at 220v)
Wild Guess: Given I can charge at 10kw, ImportLimitCurrent must be per phase, so perhaps I am maxing out one of the Phases.
Should I ask the installer to enable "Balance Load" and if that doesn't fix it, perhaps increase the ImportLimitCurrent to something a little higher like 040.0A.
Or am I barking up the wrong tree?
Posted: Sat Oct 11, 2025 1:07 pm
by WyndStryke
spammenotinoz wrote: ↑Fri Oct 10, 2025 11:43 am ...
Out of curiosity, does it give you the same figure for battery capacity as before, or is the battery capacity show as 10% lower than it used to?
(I'm wondering if they've moved to a hidden-reserve, which is how 100% DoD batteries normally work, in which case it's just the way it is reported).
If they're actually letting you set reserve to 0%, and there's no hidden reserve, not sure how comfortable I am about that.
Posted: Sat Oct 11, 2025 9:31 pm
by spammenotinoz
Great question, where can I check that.
Battery Details -> Health -> Capacity = --
Posted: Tue Oct 14, 2025 5:44 am
by spammenotinoz
Update:
During Force Charge today, battery started discharging today to provide the delta. Reduced house load to 8kw and battery started charging at 3kw. Stopped house load and battery charged at 9.1kw.
No response from FoxEss Support.
Following Up with Installer, but no fix yet.
Anyone else experienced similar charging an EV or otherwise during FREE Hours?
Posted: Fri Dec 05, 2025 12:44 am
by spammenotinoz
Update:
Resolved: After powering down the inverter and battery, then bringing them up. The new settings applied.
Simply updating Grid Import from 22A to 50A and a standard stop\start was not sufficient.
Posted: Mon Dec 15, 2025 11:52 pm
by MDJ80
spammenotinoz wrote: ↑Fri Dec 05, 2025 12:44 am Update:
Hi i have the exact smae issue as you. I have a H3 -15.
I got i little lost when you say the max grid import was set to 31.9a ( same as mine) then you changed this setting from 22a to 50a. Are we talking the same setting and simply updating from the 31.9 A to 50A
Posted: Tue Dec 16, 2025 9:17 am
by spammenotinoz
On the Inverter Front Panel, there is a setting called "Max Grid Import Current", to resolve the issue this was changed to "50a". This by-itself did not immediately fix the issue.
FoxESS also updated Master to v1.36 and performed a restart.
With my 10kw Inverter during the FREE window, I have pulled 32kw from the grid (133a), previously I could not pull more than 10-11kw.
This high-load isn't typical, was for testing.
PS: Not that it impacts myself or your use case, but I have also since learnt EPS loads (are always drawing from the inverter), as such if high they can reduce your charging speeds.
