Double Bubble Battery Banks
Posted: Sun Apr 02, 2023 4:15 pm
Although my installer sold me eight HV2600, Fox, when I contacted them about some weird system behaviour, told me the maximum ought to be seven. They suggested eight may give over voltage issues and I can confirm I did get occasional battery over voltage alarms. I also found the battery capacity meter to be wildly inaccurate with the supposed 20kWh capacity of eight batteries plummeting to around 40% (60% or 12kWh claimed to have been used) with a calculated draw of only around 4 to 5kWh (1.5kW for about 3 hours). When charging, at say 2.5kW, the capacity meter would suddenly leap to full (99%) in around 2 hours thus confirming my consumption had indeed been around 4 to 5 kWh and NOT the 12kWh claimed by the capacity meter. Reducing the stack to 7 batteries vastly improved the accuracy of the capacity meter although it was still imperfect. I can therefore concur that 8 batteries, whilst they do work, can result in wildly inaccurate capacity readings AND throw up occasional battery over voltage alarms. Note that my capacity meter NEVER showed 100% with 8 x HV2600 V1.
Being aware of the standing plans for power outages (see your leccy bill for the little square symbol with your rota disconnection letter if that threat seems like BS to you) I decided to expand my system with a second bank of HV2600 and so lashed out on a V2 BMS and seven V2 batteries.
I installed a 500V x 125A four pole, interlocked single throw changeover switch to switch from battery bank A (original V1 batteries) to bank B (the new V2 batteries) then the common on to the new V2 BMS battery input terminals. The "data" leads were fed to a 2 way manual "ethernet" switch to changeover data from battery stack A to B. The "power" leads are Pylontech AWG4 so well over engineered by at least 100% and come with the correct SURLOK connectors ready fitted, being cheaper than I could buy the connectors alone!
To change over I first power down the BMS and throw its battery breaker switch to OFF (right). Next, I throw the data switch from A to B (or vice versa) then throw the four pole power switch from A to B (or vice versa). I then throw the BMS battery breaker to ON, restart the BMS and I'm on the other battery stack. It can take several minutes for the app to respond to the changeover but that's due to its sampling rate of something like 6 x per hour.
I've learned that the capacity meter is then sometimes slightly confused for a while until the chosen battery bank discharges somewhat and recharges. It then reads perfectly! Killing the entire system (PV off, AC off) for a few minutes whilst the BMS is powered down avoids the battery capacity hiccup but I've decided to live with that small irritation as it corrects itself in a while and once recharging begins.
My capacity meter is now as accurate as I could have wished for. 7 batteries have a capacity of 17.92kWh but let's call it 18 for ease of figures. I drew them down to 40% (roughly 11kWh used) then the next day they recharged, taking 11kWh, (according to the Fox app) to reach 100%. Yes! The capacity meter now reads 100% (not 99) and the calculated draw and charge figures all agree.
It appears to me that the new BMS/battery combination is by far more accurate than the V1 with Version C batteries. I'll compare with the older batteries after these new ones, stack B, have had a month or so to "bed in". I also appear to have a minimum of 2 x 16kWh useable battery stacks and feel I no longer need to keep 35 or 40% in reserve for the dreaded power outages they keep promising us.
Min SOC 10%
Min SOC on Grid 17%.
So they system is now:
H1-3.7-E Inverter Hardware Version : -Master : 1.54; Slave : 1.02; Manager : 1.57
15 x 330W panels (6 + 9)
BMS V2
7 x HV2600 V1(C)
7 x HV2600 V2
Necessary changeover switching.
Empty savings account.
I also have 1 x HV2600 V1(C) battery either to flog or keep as a spare. I'm in North East England if anyone's interested in an extra battery.
George
Retired (National Grid Pensioner) Comms & Instrumentation Tech
Being aware of the standing plans for power outages (see your leccy bill for the little square symbol with your rota disconnection letter if that threat seems like BS to you) I decided to expand my system with a second bank of HV2600 and so lashed out on a V2 BMS and seven V2 batteries.
I installed a 500V x 125A four pole, interlocked single throw changeover switch to switch from battery bank A (original V1 batteries) to bank B (the new V2 batteries) then the common on to the new V2 BMS battery input terminals. The "data" leads were fed to a 2 way manual "ethernet" switch to changeover data from battery stack A to B. The "power" leads are Pylontech AWG4 so well over engineered by at least 100% and come with the correct SURLOK connectors ready fitted, being cheaper than I could buy the connectors alone!
To change over I first power down the BMS and throw its battery breaker switch to OFF (right). Next, I throw the data switch from A to B (or vice versa) then throw the four pole power switch from A to B (or vice versa). I then throw the BMS battery breaker to ON, restart the BMS and I'm on the other battery stack. It can take several minutes for the app to respond to the changeover but that's due to its sampling rate of something like 6 x per hour.
I've learned that the capacity meter is then sometimes slightly confused for a while until the chosen battery bank discharges somewhat and recharges. It then reads perfectly! Killing the entire system (PV off, AC off) for a few minutes whilst the BMS is powered down avoids the battery capacity hiccup but I've decided to live with that small irritation as it corrects itself in a while and once recharging begins.
My capacity meter is now as accurate as I could have wished for. 7 batteries have a capacity of 17.92kWh but let's call it 18 for ease of figures. I drew them down to 40% (roughly 11kWh used) then the next day they recharged, taking 11kWh, (according to the Fox app) to reach 100%. Yes! The capacity meter now reads 100% (not 99) and the calculated draw and charge figures all agree.
It appears to me that the new BMS/battery combination is by far more accurate than the V1 with Version C batteries. I'll compare with the older batteries after these new ones, stack B, have had a month or so to "bed in". I also appear to have a minimum of 2 x 16kWh useable battery stacks and feel I no longer need to keep 35 or 40% in reserve for the dreaded power outages they keep promising us.
Min SOC 10%
Min SOC on Grid 17%.
So they system is now:
H1-3.7-E Inverter Hardware Version : -Master : 1.54; Slave : 1.02; Manager : 1.57
15 x 330W panels (6 + 9)
BMS V2
7 x HV2600 V1(C)
7 x HV2600 V2
Necessary changeover switching.
Empty savings account.
I also have 1 x HV2600 V1(C) battery either to flog or keep as a spare. I'm in North East England if anyone's interested in an extra battery.