Charging up to 12% between 4:30 and 5:00 am
Posted: Wed Aug 27, 2025 3:05 pm
by Kiran84
There seems to be an issue with charging up before sunrise. I have my mode schedule set to charge with the following settings:
Work mode: Force Charge
Min SOC on grid: 10%
Max SOC:12%
Forced discharge cutoff soc (FDSOC): 30%
MAX. AC power for forced discharge (FDPwr): 4000W
The only other entry in my mode scheduler is Forced discharge, min SOC on grid 10%, FDSOC 30%, FDPwr 4000W. This works fine on its own and discharges to 30% as required.
When I introduce the Forced charge, albeit the battery has already reached 10% prior to 4:30am, the system charges up past 12%, reaching 15% on grid before sunrise at which point PV is sufficient to take over charge.
I reset the system in the morning when i wake up (prior to sunrise) to stop the battery from charging and this resolves the problem.
I reset and submit mode scheduler and the battery stops charging from the grid at the point. By mid-day the battery is usually fully charged however for some reason at 3pm the battery starts discharging (currently sitting at 96% as I type) despite PV being sufficient to supply the load. So i have to reset the system again in the afternoon after which the battery charges up to 100% as required.
This problem has happened every day through this week and only happens if I have the charge period enabled in mode scheduler. The discharge works fine on its own.
Does anyone know why this is happening?
Min SOC and battery reserve capacity both set to 10% in my system.
Re: Charging up to 12% between 4:30 and 5:00 am
Posted: Wed Aug 27, 2025 3:17 pm
Can you post a picture from your app of your scheduler settings please (particularly the times).
For force charge, FDSoC and FDPwr are not used and are ignored (but they have to be entered as a valid number).
If you could also let me know what inverter model you have, and if you go to the ‘Device’ tab in the app, click on ‘Inverter’ and then click on the serial number below the inverter picture it will give you some settings - can you list your Master and ARM versions.
Posted: Wed Aug 27, 2025 3:26 pm
by Kiran84
See attached
Posted: Wed Aug 27, 2025 4:00 pm
You are definitely running old versions of firmware, the schedules were only introduced around these versions and there were quite a few ‘undesirable features’ when released - I think a good starting point would be to get the firmware updated - latest is Master 1.47 and ARM 1.45, your installer should do this for you - but you can raise a support ticket in the app ‘Me’, ‘Contact Us’, ‘Support’ and ask for your inverter firmware to be updated.
Can I ask why you are using maxsoc of 12% in the force charge from grid, that would/should restrict the charge to no more than 12% soc which is only a very small amount above your minsoc (10%)
Posted: Wed Aug 27, 2025 4:59 pm
by Kiran84
I only need 2% in the morning from 5am to 7.30am when PV takes over to charge the battery.
2% will increase in winter I'm sure.
Have contacted my installer to upgrade the firmware and will let you know if that fixes the issue.
Posted: Wed Aug 27, 2025 6:18 pm
Ok once you are updated let us know how you get on.
Posted: Mon Sep 01, 2025 4:32 pm
by Kiran84
Been updated but still not working as expected.
Firmware updated on 29/8/25 and I now have the following versions installed: Master 1.47, slave: 1.01, ARM: 1.45.
The problem seems to have started when I introduced charging period and when I allowed the battery to discharge below 15%, the inverter doesn't seem to behave as expected.
On 30/08/25 @ 2am: The battery discharges to 12% and there is a pulse charging up to 13%. Why doesn't it go down to 10% min SOC on grid?
There are a series of pulses between 2am and 5am when the battery drops to 12% that forces charge back up to 13%.
Also the discharge cycle at 4pm goes down to 25% at which point I manually reset the system to prevent further drop. This was schedules to go down to 30% so why drop to 25%?
The following day (31/8/25): I attempted to use the charge time option to set overnight charging (rather than the mode scheduler). The charge period was enabled between 04:55 and 05:00 and a spike is visible charging from 13% to 19%. Prior to this, the battery drops to 10% at 01:00 and the system auto charges back up to 15%. Why does it do this?
The discharge cycle at 4pm goes below scheduler setting of 30%. I was not home in time to do the manual reset this time and the battery discharged all the way down to 10%. Again why drop below 30%?
Posted: Fri Oct 10, 2025 10:11 am
by Kiran84
Resolved this issue.
There seems to be a minimum requirement to charge 5% above min SOC.
So in my case, I have min SOC set to 10% and must charge up to 15%. If I set a schedule that only charges up to 12% then the system seems to behave strangely through out the day.