Feed-in priority question

Posted: Thu Jun 26, 2025 9:42 pm
by RussJH
2 x 10kw EP11 owner and now having 16 Panels installed tomorrow so I am setting up my feed-in priority in readiness.

I want to use PV output and batteries during the day, export excess solar, and no battery charging (this is done overnight at 7p)

I've set the feed-in priority as follows :-

Min SOC on grid - 10%
Max SOC - 100%
Forced discharge cut off - 10%
Max AC power for forced discharge - 0w

I am unsure about Max SOC setting at 100% and how this affects the routing of excess solar ouput ? Should I lower this - we generally use about 50% battery during the day pre-solar install.

Many thanks

Russell

Re: Feed-in priority question

Posted: Fri Jun 27, 2025 12:06 am
by WyndStryke
That looks fine to me, the surplus solar will go to the grid. I'd leave Max Soc at 100%.


The FD Soc and FD Power are ignored unless the mode is Force Discharge.