RS485 Connections to Dual Inverters for Home Assistant

Posted: Fri Oct 11, 2024 12:25 pm
by DoingMyBit
Hi All,

I've a recent install of solar + batteries. Due to the array size we are running dual inverters that should be running in parallel. My installer is coming back for a few snags shortly, and I'd like him to wire in the connections for RS485 to the inverters so that, if I choose at a later date to use Home Assistant, the wiring at that end is already done.

My question is, do the RS485 cable pairs need to wired into each inverter (ie. ending up with 2x RS485 connections to connect into later), or just the inverter set up as the Master?

Thanks!

PS. Sorry if the terminology is incorrect - I'm a newb!

Re: RS485 Connections to Dual Inverters for Home Assistant

Posted: Fri Oct 11, 2024 12:29 pm
by Will
Hey,

So you'll want two cables (RS485A & RS485B) terminated into the correct pins (pin 3 & 4) on the coms port PER inverter. So if done correctly, you'll have a network cable coming from each inverters com port with two wires ready to be used in future.
You'll want to use a modbus to IP adapter per inverter not trying to daisy chain them.

See page 22 of the manual attached.

Re: RS485 Connections to Dual Inverters for Home Assistant

Posted: Fri Oct 11, 2024 9:20 pm
by DoingMyBit
Thanks Will - super helpful!