Myenergi Zappi automation to protect hybrid battery during Eco Tariff

User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Oops!!

I spoke too soon. I must have selected the working version (AutomationOne) not the trial version (AutomationTest). I'm afraid AutomationTest doesn't work. I get the first notification that the automation has triggered but nowt else.

Again for reference, this is the code for the working version.

Code: Select all

alias: FD_AutomationOne
description: Triggers when fixed low tariff period starts.
triggers:
  - trigger: time
    at: input_datetime.fd_setlowtariffstart
conditions: []
actions:
  - action: notify.persistent_notification
    metadata: {}
    data:
      message: FD_AutomationOne has triggered
  - variables: {}
  - action: timer.start
    metadata: {}
    data:
      duration:
        hours: "{{ states('input_number.fd_waithours')}}"
    target:
      entity_id: timer.fd_timerone
  - action: notify.persistent_notification
    metadata: {}
    data:
      message: FD_TimerOne has started
mode: single
Regards, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

I've not used the timer.start etc.. function - my reading of the timer is that it will start the timer fd_timerone and that should start timerone counting down with the duration you've just set.

So looking at your automation when the time is fd_setlowtariffstart

- you would expect to get a notification
- then your timer start
- then another notification

and at some point I guess in another automation you catch timerone finish ?

But as you are only getting one notification the timer 'action' must have had an error ?

Do you see anything in your logs (Settings, System, Logs) or when in the automation you can click on 'TRACES' in the top right hand corner and that shows you what happened when it last triggered (I guess the trace timeline will probably show an error)
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

You are right, there is an error flagged in Traces.


Notifications 'Send a persistent notification'
Timer 'Start' on FD_TimerOne
Stopped because an error was encountered at 25 January 2025 at 16:51:37 (runtime: 0.00 seconds)

offset 2.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.12.1 should be format 'HH:MM', 'HH:MM:SS' or 'HH:MM:SS.F' for dictionary value @ data['duration']

I have no idea what the sequence of numbers is about but perhaps you do? Actually on checking, the value of FD_TimerDuration at 16:51 it will have been very close to 2.12 hours. Why it repeats is still a mystery. Looking for a string terminator? Dunno.

I will have another go and try parsing the output of FD_TimerDuration into integer hours and integer minutes and passing these as strings. Can you give me an idea how to make sure the output is made into a string?

Thanks again. Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

ok, i've just had a crash course on timers and this is what i've found.

Firstly despite the documentation not mentioning it, it does support the member keys `hours:, minutes:, seconds:` so you can do exactly what you are doing and it should work so we're into the wonderful world of template conversions and how objects convert in real time.

The second thing to mention is that the template test tool isn't the best in that it's an interactive line by line interpreter, it doesn't always resolve as you would expect when it appears to work here - largely depending on how it is interpreted by the real time object when doing the conversion in your code.

I've written a timer and used a number to set it just as you did and it works fine - so I am sure that your syntax is correct. What must not be correct is the contents of the number or the type or the step doesn't match the type which is upsetting the conversion, whatever it is, it is upsetting the interpreter used when the template resolves the hours: {{ }}

So I suspect this might work as it relies on a type conversion being handled outside of the template and then simply resolves a variable in the template and doesn't have to face the complexity of converting a number. (The default=0 just forces the return of 0 if the number is unavailable so that it doesn't generate an error if the number isn't available ~ startup for example).

Code: Select all

action: timer.start
metadata: {}
data:
  duration:
    hours: "{% set myVar=states('number.fd_timerduration')|round(2,default=0) %}{{ myVar }}"
But I also think modifying your number template to convert the result of the template with a final round(2) might also fix this - if you are specifying a step make sure it is '0.01' i.e. 2 decimal places (i'm assuming you want that for accuracy), obviously if you want it to 1 decimal place then keep the round(s) at 1.

Code: Select all

{# Read target end time in decimal hours #}
{% set EndHours = states('number.fd_windowstarttime') %}
{# Read target begin time in decimal hours #}
{% set BeginHours = states('number.fd_timenowasdh') %}
{# Calculated timer duration in decimal hours #}
{% set myDuration = (((EndHours | float ) - (BeginHours | float)) | round(2)) %}
{# Adjust if duration is negative #}
{% if myDuration < 0 %}
{% set myDuration = (myDuration + 24) %}
{% endif %}
{{ myDuration|round(2) }}
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

Bingo! For sure this time. With your modified code in AutomationTest, triggering it produces both notifications including the all important 'FD_TimerOne has started'.
That device of defining a variable in the jinja line and then passing the variable back to yaml is inspired! Most of my difficulties come about because of confusing jinja and yaml. Jinja I can just about cope with, it is more similar to the old style programming like C that I am - or used to be - familiar with. Yaml is something else entirely!

Thank you so much for all the trouble you have taken. I also think that your technique should be publicised in some way. I have no idea how but it opens up lots of possibilities having, in effect, a recursive timer.

Impressed and grateful.
Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

great, glad it's working !

Must admit I really like the way that timer works, it's very efficient - i'm going to have to find some ways to use it :)
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

More questions I'm afraid. I have made a little progress with my ongoing automation saga but once again run up against the brick wall of my ignorance of yaml and jinja.

This is the code I have that isn't working:

Code: Select all

alias: FD_AutoTwoTest
description: ""
triggers:
  - trigger: state
    entity_id:
      - timer.fd_timerone
    from: active
    to: idle
conditions:
  - condition: state
    entity_id: input_boolean.fd_onoffswitch
    state: "on"
  - condition: numeric_state
    entity_id: number.fd_energyforexport
    attribute: min
    above: 1
  - condition: template
    value_template: >-
      {{((states('number.fd_expwinmaxduration') | float(2)) -
      states('number.fd_expwinminduration') | float(2)) >= 0.5  }}
actions:      
  - action: >
      {% if states('number.fd_expwinmaxduration') | float(2)) - states('number.fd_expwinminduration') | float(2)) <= 0.5  %}
        notify.persistent_notification
        metadata: {}
        data:
          message: FD_AutomationTwo has triggered.Start Exporting!
      {% else %}
        notify.persistent_notification
        metadata: {}
        data:
          message: FD_AutomationTwo has triggered. Not ready to export
      {% endif %}
mode: single
And this is the error message it generates.
Message malformed: Service {% if states('number.fd_expwinmaxduration') | float(2)) - states('number.fd_expwinminduration') | float(2)) <= 0.5 %} notify.persistent_notification metadata: {} data: message: FD_AutomationTwo has triggered.Start Exporting! {% else %} notify.persistent_notification metadata: {} data: message: FD_AutomationTwo has triggered. Not ready to export {% endif %} does not match format <domain>.<name> for dictionary value @ data['actions'][0]['action']

If you wouldn't mind having a look and finding my mistakes.

Many thanks, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

I don't think that would work, you can't have multiple data: elements in an action the interpreter will get very upset (and you've a problem with the number of brackets), but you should be able to do it like this by modifying the data you return in the message:

Code: Select all

alias: FD_AutoTwoTest
description: ""
triggers:
  - trigger: state
    entity_id:
      - timer.fd_timerone
    from: active
    to: idle
conditions:
  - condition: state
    entity_id: input_boolean.fd_onoffswitch
    state: "on"
  - condition: numeric_state
    entity_id: number.fd_energyforexport
    attribute: min
    above: 1
  - condition: template
    value_template: >-
      {{((states('number.fd_expwinmaxduration') | float(2)) -
      states('number.fd_expwinminduration') | float(2)) >= 0.5  }}
actions:      
  - action: >
        notify.persistent_notification
        metadata: {}
        data:
	  message: >
            {% if (states('number.fd_expwinmaxduration') | float(2) - states('number.fd_expwinminduration') | float(2)) <= 0.5  %}
            FD_AutomationTwo has triggered.Start Exporting!
            {% else %}
            FD_AutomationTwo has triggered. Not ready to export
            {% endif %}
mode: single
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

Many thanks for your help again. I think I should have explained a bit more what I'm actually trying to achieve.
The code I sent shouldn't have included the 3rd condition. That test is actually the test for whether or not to start forced discharge and should be in the if then else bit.

The notifications are just there to act as placeholders while I test the logic.

The actual flow is meant to be:

Automation is triggered by my timer
Uses conditions to check if the on/off switch is on and that the amount of stored energy is over a minimum.

Then the meaty bit,
If the max export window duration <= (min export window duration + 0.5)
then
set max battery discharge current
set inverter work mode to forced discharge
else
start my timer and set duration to a specified time.

So I don't really care about the notification messages, they are just to help me check each time I make a change to the code. I think from looking at the code you wrote earlier in this thread it should be possible to use logbook entries in place of the messages?

The key thing I am trying to understand is how to use if then else conditional statements within the automation to control which actions occur.

Regards, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

The timer state change will trigger the automation

Conditions only give you basic tests, so it is best to use the initial conditions for only the basic stop / go things like your on_off switch and minimum energy

You then do all the meaty stuff in the actions, but using the action
‘if-then’
IMG_1699.jpeg
within that ‘if then’ you set the conditions for the ‘if’ such as ‘

If the max export window duration <= (min export window duration + 0.5)’

And your actions would then be

Set max battery discharge current (number:set)

Code: Select all

action: number.set_value
metadata: {}
data:
  value: "5"
target:
  entity_id: number.force_discharge_power

Set inverter work mode to force discharge

Code: Select all

data:
  option: Feed-in First
target:
  entity_id: select.work_mode
action: select.select_option
Then ‘Add else’ to add and else to the ‘if’

And add the action to start your timer in there.

You can nest ‘If then / else’ by adding more of them within the IF’s actions as needed.

Also because single conditions don’t give you enough flexibility you can add an OR or AND conditions and then have multiple conditions within where they only need 1 to be true for the OR or all need to be true for the AND.
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Thanks Dave,

Brain fog now so I will hit the keyboard again in the morning. But, one final question today. In the 'if' statement I am using template number helpers and doing some arithmetic. Do I need to use a jinja template or can I just plug in the states('fd_expwinmaxduration') etc into the automation?

Cheers, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

HughInDevon wrote: Thu Jan 30, 2025 7:05 pm Thanks Dave,

Brain fog now so I will hit the keyboard again in the morning. But, one final question today. In the 'if' statement I am using template number helpers and doing some arithmetic. Do I need to use a jinja template or can I just plug in the states('fd_expwinmaxduration') etc into the automation?

Cheers, Hugh
No problem it drives you up the wall sometimes :)

Using the ‘If Then’ action you can add a condition and then use a template (much easier to test) and no need for jinja.
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,
As usual, here is my daily dose of 'why doesn't it work'.
I have followed your suggestions (at least I think I have) and I now have a semi-working automation that follows the logic I wanted. I have not yet tried to add the actual code to make the forced discharge happen but I have added the code for the timer that is supposed to keep checking every 30 minutes. When I run the automation it behaves OK, it sends the expected notification and it starts the timer. So far so good BUT it only does it once. In theory the timer changing from active to idle should restart everything and so there should be a second notification, then a third etc. until the first condition is met and everything stops.

Here is the code:

Code: Select all

alias: FD_AutoTwoTest
description: ""
triggers:
  - trigger: state
    entity_id:
      - timer.fd_timerone
    from: active
    to: idle
conditions:
  - condition: state
    entity_id: input_boolean.fd_onoffswitch
    state: "on"
  - condition: numeric_state
    entity_id: number.fd_energyforexport
    attribute: min
    above: 1
actions:
  - if:
      - condition: template
        value_template: |-
          {{((states('number.fd_expwinmaxduration') | float(2)) -
                states('number.fd_expwinminduration') | float(2)) <= 0.5  }}
    then:
      - action: notify.persistent_notification
        metadata: {}
        data:
          message: Ready to start forced discharge.
    else:
      - action: notify.persistent_notification
        metadata: {}
        data:
          message: Not ready for forced discharge. Start the timer to check later
      - action: timer.start
        metadata: {}
        data:
          duration:
            minutes: "{{ states('input_number.fd_setcheckevery')}}"
        target:
          entity_id: timer.fd_timerone
mode: single
So, I am sorry to be such a nuisance but once again I need some help!

Thanks, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

There’s a number of things that will stop the timer being reset, i’ll say what I can see and then you can tell me if that’s what you are expecting.

The automation activates when the timer goes from active to idle

It can only proceed further if fd_onoffswitch is on AND fd_energyforexport is greater than 1

Both of those conditions must be met to go any further.

Assuming they are met

You are basing your IF on this template being true {{ ((states('number.fd_expwinmaxduration') | float(2)) - states('number.fd_expwinminduration') | float(2)) <= 0.5 }}

If it is true you’ll send a message

If it is false you will send a message and reset the timer.

The one test that might be failing when it goes idle is the fd_energyforexport greater than 1 if it isn’t true you won’t get any messages and the timer won’t be reset.

The other thing i’m not sure about is how does the timer start for the first time i.e. how do you make it go active in the first place so that it triggers the automation ?.
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

Thanks for your reply and my apologies for not responding sooner. We had various car problems that cast a blight on the evening. Picking up a loan car this morning while ours is in for repairs - although I have my doubts, the main dealership we bought it from don't seem to have a clue about EVs.

So, to answer your questions.

There’s a number of things that will stop the timer being reset, i’ll say what I can see and then you can tell me if that’s what you are expecting.

The automation activates when the timer goes from active to idle

It can only proceed further if fd_onoffswitch is on AND fd_energyforexport is greater than 1

Both of those conditions must be met to go any further.

Assuming they are met


These conditions are definitely met.

You are basing your IF on this template being true {{ ((states('number.fd_expwinmaxduration') | float(2)) - states('number.fd_expwinminduration') | float(2)) <= 0.5 }}

If it is true you’ll send a message

If it is false you will send a message and reset the timer.


Correct. The IF template is never true during testing so the timer does get reset and I get a notification that this has happened. I have also checked the timer directly and it is running and counting down from the preset value it has beem set to (30 minutes usually).

The one test that might be failing when it goes idle is the fd_energyforexport greater than 1 if it isn’t true you won’t get any messages and the timer won’t be reset.


This is always true during testing as is shown by the timer getting reset and starting.

The other thing i’m not sure about is how does the timer start for the first time i.e. how do you make it go active in the first place so that it triggers the automation ?.

The timer is started in the first instance by another, simple, automation. The code for that automation is:

Code: Select all

alias: FD_AutomationOne
description: Triggers when Octopus Intelligent Go fixed low tariff period starts.
triggers:
  - trigger: time
    at: input_datetime.fd_setlowtariffstart
conditions: []
actions:
  - action: notify.persistent_notification
    metadata: {}
    data:
      message: FD_AutomationOne has triggered
  - action: timer.start
    metadata: {}
    data:
      duration:
        hours: >-
          {% set myVar=states('number.fd_timerduration')|round(2,default=0) %}{{
          myVar }}
    target:
      entity_id: timer.fd_timerone
  - action: notify.persistent_notification
    metadata: {}
    data:
      message: FD_TimerOne has started
mode: single
This uses your clever way of setting the duration with a number template. It works a treat!

So, I am at a complete loss as to why in AutomationTwo the timer is started with a set duration but does not trigger the automation when it finishes. Is there some weird checking to prevent the possibility of creating an infinite loop?

Regards, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

Ok thanks, understand how it starts off now.

The only way I can see that you won't get any notifications when the timer goes from active to idle is if those initial conditions are stopping it - anything else would generate a message.

Just a couple of things to note when you run an automation it ignores triggers and conditions and simply runs the actions - so running it will always work, the trigger state however being true would have to see both of those conditions as true for it to do anything.

I think the thing to do is set your timer active with your simple automation - then go to your main automation and open it in the editor - on each of the two conditions click the 3 dots on the right hand side of them and choose 'Test' - this will execute the condition as a test and will tell you what the return state is.

If either of those 2 conditions says 'Condition does not pass' it's that condition that is stopping any further processing from happening.
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

Thanks for that. You are right. When I do the testing, it fails on my second condition, number.fd_energyforexport is greater than 1.

I guess this is because number.fd_energyfor export is a template helper. I will try and redo the automation to take this into account. I'll let you know how I get on. Fingers crossed!

Regards, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

I have tried to redo the automation from the UI but no joy. The latest version is here:

Code: Select all

alias: FD_AutomationTwo
description: ""
triggers:
  - trigger: state
    entity_id:
      - timer.fd_timerone
    from: active
    to: idle
conditions:
  - condition: state
    entity_id: input_boolean.fd_onoffswitch
    state: "on"
  - condition: numeric_state
    entity_id: number.fd_energyforexport
    above: 1
    value_template: "{{\"states(number.fd_energyforexport)\"}}"
actions:
  - if:
      - condition: template
        value_template: |-
          {{((states('number.fd_expwinmaxduration') | float(2)) -
                states('number.fd_expwinminduration') | float(2)) <= 0.5  }}
    then:
      - action: notify.persistent_notification
        metadata: {}
        data:
          message: Ready to start forced discharge.
    else:
      - action: notify.persistent_notification
        metadata: {}
        data:
          message: Not ready for forced discharge. Start the timer to check later
      - action: timer.start
        metadata: {}
        data:
          duration:
            minutes: "{{ states('input_number.fd_setcheckevery')}}"
        target:
          entity_id: timer.fd_timerone
mode: single
The only change I can see is the addition at line 16 of value_template: "{{\"states(number.fd_energyforexport)\"}}"

But when I set it going and test this condition I get a CONDITION DID NOT PASS in white letters on a grey background.

If you would be kind enough to have a look and see where I am going wrong?

Regards, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

It looks like you've got something in the value template at the bottom of the condition - that should be blank all you need with a numeric check is the entity id and the value

i.e. it would look this in yaml

Code: Select all

- condition: numeric_state
  entity_id: number.fd_energyforexport
  above: 1
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Brilliant. The automation is now cycling as it should!

Ta Everso!

Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

Waiting for my installer to update the inverter firmware before I try and finish my force discharge automation. In the meantime I am exploring using logbook to record stuff. I am trying to make a log entry that adds a sensor value to some text so I get something like "EV charging added " + value from sensor.myenergi_zappi_20494256_charge_added_session. My (naturally) non-working code is here:

Code: Select all

alias: EV Charge Logging
description: ""
triggers:
  - trigger: time
    at: input_datetime.logbook_test
conditions: []
actions:
  - action: logbook.log
    metadata: {}
    data:
      name: EV Charging
      message: >-
        EV Charging used   
        {{states('sensor.myenergi_zappi_20494256_charge_added_session.state')}}
      entity_id: sensor.myenergi_zappi_20494256_charge_added_session
mode: single
If you wouldn't mind having a look?

Thanks, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Dave Foster
Posts: 1855
Joined: Thu Oct 13, 2022 7:21 pm

Hi Hugh,

almost there, in templates you don’t need to add the ‘.state’ if you use states(‘xxx’) it assumes state you don’t need to add it (unlike javascript where you do) - this would be the logbook code -

Code: Select all

action: logbook.log
metadata: {}
data:
  name: EV Charging
  message: |-
    EV Charging used   
      {{states('sensor.myenergi_zappi_20494256_charge_added_session')}}
  entity_id: sensor.myenergi_zappi_20494256_charge_added_session
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

So close but so far! Thanks as always for the much appreciated help. I am making progress, honest - but it's painfully slow.

Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,

I am getting closer - but.......
This is the code that isn't working. My problem is that I can't find a way to specify the work mode I want, force discharge, in the UI and when I try it directly in yaml it doesn't like it. Here is my non-working code.

Code: Select all

alias: AutoTwoTest
description: ""
triggers:
  - trigger: state
    entity_id:
      - timer.fd_timerone
    from: active
    to: idle
conditions:
  - condition: state
    entity_id: input_boolean.fd_onoffswitch
    state: "on"
  - condition: numeric_state
    entity_id: number.fd_energyforexport
    above: 1
actions:
  - if:
      - condition: template
        value_template: |-
          {{((states('number.fd_expwinmaxduration') | float(2)) -
                states('number.fd_expwinminduration') | float(2)) <= 0.5  }}
    then:
      - action: notify.persistent_notification
        metadata: {}
        data:
          message: Ready to start forced discharge.
      - action: number.set_value
        metadata: {}
        data:
          value: "5"
        target:
          entity_id: number.kh10_inverter_force_discharge_power

      - device_id: 9ad62b0d2a58f387f254fc2ad8e39781
        data:
          option: force_discharge   
        domain: select
        entity_id: select.kh10_inverter_work_mode
        action: select.kh10_inverter_work_mode
    else:
      - action: notify.persistent_notification
        metadata: {}
        data:
          message: Not ready for forced discharge. Start the timer to check later
      - action: timer.start
        metadata: {}
        data:
          duration:
            minutes: "{{ states('input_number.fd_setcheckevery')}}"
        target:
          entity_id: timer.fd_timerone
mode: single
As always a pointer or two as to where I am going wrong would be much appreciated.
Thanks again, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
User avatar
HughInDevon
Posts: 67
Joined: Wed Jul 31, 2024 4:50 pm

Hi Dave,
I think I have cracked how to start forced discharging. I managed to do it via the UI after a bit of trial and error. So, my last remaining problem is how to stop the fd before the soc falls to 10%. Ideally I would like to stop it in the same automation when the Soc drops to say 15% but perhaps I need to use another automation to stop it? Any thoughts?

Regards, Hugh
KH10 with 4 off ECS4800 batteries.
20 Jinko 435W panels in 2 strings. 10 on house, south facing, 10 on barn, east facing.
Solar installation active on 27/11/2024. Export MPAN active on 30.12/2024.
Zappi V2 charger and 2 EVs.
Currently on Octopus Intelligent Go tariff.
Home Assistant modbus integration (Now working - ish)
Post Reply