Re: Off grid setup with Generator backup supply
Sure, I'll send a few pics and description and/or diagram.
KH 10.5
24 x 480w PV panels N/S
8x ECS4800v2
W4 Datalogger
Home Assistant via Modbus
Sussex
--ignore--
KH 10.5
8x ECS4800v2
W4 Datalogger
Sussex
I am not an electrician! But this mod was done by a licensed electrician, though more or less my 'design' as faciliated by prevoius posts in this thread -- thanks again to all!
Since my set up was originally designed with full house load (minus car charger) connected via EPS connection of inverter, to run off batteries when the grid is down and inverter isolates from the grid, I had an earth rod installed.
I think it is important to have an earth rod installed when running house loads from a generator since without the grid there is no earth. The chassis of the generator seems to be tied to the ground connector in the 32A generator output connection.
Generator has floating neutral so neutral and ground of generator are tied where they connect to the changeover switch.
I did not, and I belive my installer did not, reduce any safety settings in the inverter for this mod, and when I run on generator I get no warnings -- the KH10.5 accepts the generator as if it were the grid.
That means of course, you can easily fry the generator if the inverter starts to export / feed in power! One should manually change the maximum feed in wattage/current to ZERO before connecting generator. I would further advise very cautious use (better no use) of any high draw appliances (oven, hob, toaster, AC units) because I have noticed that when these loads come OFF, the inverter will often kick back some power to the grid briefly as it balances (even with export set to zero).
My intended use of the generator is only for long emergency power outages, where there is not enough solar to store in our batteries to run the house continuously (like in Winter). Hopefully this situation may never happen. But if we decided to go heat pump and remove the gas boiler, this would add peace of mind in the winter. My plan would be to use the generator to charge up the house batteries in the evening when the sun has gone down. In my brief preliminary testing, I could charge the FoxESS batteries when the inverter is supplied by the generator -- but of course you have to set the Inverter charge current to something low and suitable for your generator's capacity.
Simplified Wiring Diagram
Generator and Cable
Generator and Cable
Gen and Inverter meters
Gen outdoor connector
Lewden changeover switch
KH 10.5
8x ECS4800v2
W4 Datalogger
Sussex
Nice write-up, thanks for sharing!
"Everything that doesn’t have a decent survival rate will reset, for example the cooker clock resets, the TV turns off, etc. So if you have, say, a desktop PC and no UPS, yes it will likely turn off. It’s not 50ms for the EPS to come back on, definitely feels a lot longer."
I ran my off-grid setup originally on a manual transfer switch and it was 50:50 if the changeover was fast enough to keep the clock and network gear on. Last year, I switched to a smart ATS and it has been transformational. It's not an expensive unit, an enclosure DIN rail 2P 125A unit costs around £60 (incl. enclosure). The smart features allows me to operate the switch from an app or from a Home Assistant integration. So, I have the switch fully automated via the Home Assistant to switch between mains and solar depending on the battery SOC and available sunshine.
No more guesswork needed working out if there is enough battery to see through the night. If you have a smart generator than that could be tied into the Home Assistant module to turn the generator on a few seconds before automatically triggering the transfer switch.
My EPS box has a second input labelled "inverter 2".....
Following several long (7 hour+) duration power cuts where the PV and battery were fortunately sufficient I wondered if I could connect a small (3kW) 230V ac generator to this input
Obviously I would need to manually start it which wouldnt be a problem and from the diagram it appears it would supply the WHOLE house load plus battery charge if, say there was no PV input so it would need limiting to 3kW...
I am forward thinking in case of more long duration power cuts where there could be no PV so the generator would effectively be "the grid" and the house would run from the battery or PV if possible with any excess loads provided by the battery and inverter as per normal, under low house load the generator would mainly be charging the battery ready for later demand
I did also consider rectifying the ac from the genny into DC (yes, I am aware of the dangers of high voltage DC and would take relevant precautions) and connecting that to one of the spare "PV" inputs, the spec says this can be 80 to 500V but internet searching discourages this idea as the DC supply would be dirty unlike the pure DC from PV or battery and the MPPT in the inverter would probably play havoc with the genny output
FOX KH7 7kw hybrid inverter
EN-EPS-BOX-SP gateway
Good to hear the Eastron meter swap and newer firmware worked in your test. Since you asked for photos or video, I'd also like to see them before wiring my own generator. Did you leave the inverter's grid profile and safety settings exactly as they were after switching the CT to the Eastron? Also, how long did it take the inverter to sync to the generator output, and did you see any frequency or voltage trips during that ten-minute run? That would help me judge whether it's worth trying on my unit.
Any thoughts on my suggestion.....