KH10 Grid Import Limit Maxed at 63Amp/14.7Kw since Version 1.69 Master Even though settings are 20kwh/80Amp
My system - KH10 63Amp CB, EQ4800 42kw battery, 80Amp House Main Circuit Breaker before when on KH10 Version 1.67 Master could import form grid at around 17.5kwh to house.
After the upgrade to Master V1.69 the max import from grid to house is around 63Amp/14.6kwh. The Inverter has the max import current still set at 80 and max power import still set at 20000W. In fox ess cloud 2.0 i have max ImportPowerLimit 20Kwh.
However the system is clearly limiting import power from grid down to around 63Amp/14.6kwh.
Has anyone else had this issue since upgrading for KH10 to Master 1.69/ Slave 1.03/ARM/Manager 1.64????
Can Fox Ess remove this imposed limit on my house grid load? Which appears to be effecting any KH10 inverter above 1.68 Master firmware level, as confirmed with other users. FOX ESS have no right to limit the power to the house, only that to the inverter.
Re: KH10 Grid Import Limit Maxed at 63Amp/14.7Kw since Version 1.69 Master Even though settings are 20kwh/80Amp
Hi you are explaining the issue very well. I have noticed exactly the same issue; I am based in the UK. My inverter and battery system is almost identical to yours. I have raised the issue to fox ess support. Unfortunately the replies I received were unsatisfactory and conyradicting themselves. The discussion ended in a promise that the issue will be addressed in the next firmware update.
Typically at night where electricity is cheap and you may want to force charge your solar batteries and at the same time charge your EV and heat the house with a heat pump or set the laundry machine etc, the KH10 inverter sees via the CT clamp that more than 63A are incoming from the grid to the house and decides for some reason that the maximum incoming current from the grid to the house should be 63A instead. For example at night you want to charge your solar battery from the grid with 50A and charge your EV with 32A and some other loads in the house with 13A. That makes a total of 95A to draw from the grid at night. If the house circuits and mains fuse are designed for a total of 100A it should not be a problem at all. However, the KH10 will see that an incomimg current to the house of 32A + 13A = 45A is in demand and will limit the maximum current it draws from the grid to force charge the solar battery to 63A - 45A = 18A, instead of 50A that you are telling it to draw.
This is clearly wrong because the KH10 assumes that the house circuitry can only handle incoming current up to 63A, which may not be the case for modern or updated houses.
Even if a user increases the maximum import limit setting in the app to more than 14500W which roughly corresponds to 63A at 230V, the inverter ignores this command. I don't know if this is done on purpose but it is not to protect the inverter. It might possibly be there to avoid users to blow up the mains house fuse if they don't know what size it is. Some forums suggest to move the CT clamp to a place in the house circuit that does not monitor the power that goes to the EV, which give a solution, but I think this is not how the fox ess system should be opetating.
Anyway, if this is a matter of correcting the problem in the next firmware update, there should be a popup warning in the app or something like that which makes sure the user setting up the maximum import limit has checked what their mains fuse size is beforehand.